hing (stays activated until manually reset from the panel.)?
Again, this defeats the purpose of the exterior waterflow signal
in the event it is activated by a temporary situation, such as a
water surge.? (Once the pressure returns to normal, or the water
flow from the surge clears, the exterior signal would still be
sounding when fire companies arrive, giving a false indication
that there is a water flow.)? For those non-fire department
operations types out there, the normal SOP for fire companies
arriving at sprinklered properties is that if the exterior
waterflow signal is sounding it assumed that water is actually
flowing and?hose is layed and connected to the FDC to support the
operating system.? If the signal is not sounding, companies
investigate first.? If water is then found to be flowing, there is
a time delay in supporting the system.
The need for a dedicated and properly identified circuit for the
120VAC exterior waterflow signal then becomes vital.? As Craig
said, your wouldn't want someone shutting down a breaker for a
toaster circuit and killing the exterior signal, especially since
there is no battery backup.? While it is true that the electrical
issue is not directly the sprinkler contractors concern, if NFPA
13 requires an exterior waterflow signal, and the electrician does
not connect it properly, most AHJs will not approve the final, and
the customer will not have an approved sprinkler system.? I think
it is in our best interest to follow through and make sure the
system meets the code and passes the acceptance test.? It is not
our function to fix the problem, only to identify the problem to
the customer so he can address the electrical contractor properly.?
(Besides, who does the customer yell at anyway?if he can't get his
CO?? LOL)??
-----Original Message-----
From: [EMAIL PROTECTED]
To: [email protected]
Sent: Wed, 18 Jul 2007 10:02 am
Subject: RE: Alarm Circuit
Your alarm devices (water flow, tamper, water pressure, alarm bells)
should be 24vdc or whatever is required to match the fire alarm
system.
Most are 24vdc, (power limited fire alarm (PLFA) circuits) and the
power
to each device comes through the fire alarm panel. You can find
some
120vAC alarm bells and tamper & flow switches but I've only come
across
them where the building wasn't equipped with a fire alarm system. If
that's what you've got then they should be on a separate circuit of
their own.
The alarm panel connection to the building power grid is really
not the
sprinkler contractors concern. That's the responsibility of the
Electrical contractor so I wouldn't worry about it.
There is considerable verbiage in NFPA 70, article 760 as well as
other
places (national electrical code) concerning rules for wiring,
conductors and on and on and on for fire alarm systems. That is
primarily where they get their direction from.
The fire alarm system should be on a dedicated circuit as stated
in NFPA
72, 4.4.1.4.1 as you found. You wouldn't want someone pulling a
breaker to shut off a toaster and kill the fire alarm system too,
(although they do have battery backup but power interruption would
render a trouble or supervisory alarm).
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
Gregory
Lindholm
Sent: Wednesday, July 18, 2007 9:31 AM
To: SprinklerFORUM
Subject: Alarm Circuit
We have always told the electricians on projects that the wiring
for the
sprinkler alarms had to be on a dedicated circuit on the panel.
Is this right, and if so, where is it stated?
I looked in the 2002 edition of NFPA #72, and the closest thing
that I
found is 4.4.1.4.1, but not sure if that is correct.
Greg Lindholm
Metro Fire Protection, Inc.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_____________________________________________________________________
___
AOL now offers free email to everyone. Find out more about what's
free from AOL at AOL.com.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)