Reza,
I like your questions, it's sort of like a quiz and after we've answered,
you post the NFPA response as the solution!
On the issue of reliability, I think Stewart and others said that there are
no absolutes. On the issue of reliability and risk, there often is no clear
prescriptive guidance. I have seen a trend toward diesels, but diesels are
maintenance intensive and for those owners not committed to the required
IT&M and without significant AHJ and/insurer oversight, I don't think it is
a slam dunk that the diesel beats the electric even when you consider power
reliability. A diesel drive pump and tank arrangement is often considered
the gold standard, but what if the water tank or diesel fuel tank is empty?

Many of the sites I've worked with have 2 water supplies. That typically
would be an electric drive paired with a diesel on the 2nd supply. The power
supply is considered sufficiently reliable for the water supply with the
electric drive to be credited as one of two supplies. You wouldn't typically
provide 2 electric drives since the goal of the redundant supplies is to
provide an improved level of reliability. That improved reliability is
enhanced with a diesel drive to address what might be a low probability of
loss of power to the electric drive. Also, there are cases where every so
many years, electrical equipment maintenance is required which forces a
planned shutdown of the electric drive pump. Having a diesel drive leaves
that pump unaffected by such maintenance.

Where is the electric power considered sufficiently reliable - on site power
generation backed up with ties to the local grid is one example from my
experience. Depending on plant size, that's 30 - 200 MW in my experience on
site with very well developed load shedding plans. Most large industrial
sites don't connect to the grid and cross their fingers. Unplanned power
outages are very costly (direct costs and the indirect and uninsurable costs
of loss of market share, brand damage, etc. when you can't supply customers
in a just-in-time business world) and there is a lot of work that goes into
the equipment, procedures, etc. to avoid unplanned outages. If there are
unavoidable planned or unplanned outages, fire pumps would be a critical
load and one of the very last to go. If you have this level of
infrastructure, equipment, load shedding plans, etc. you probably have what
might be a sufficiently reliable power supply for the electric drive.

I have gone the 2 diesel route, but I do often prefer at least one electric
drive in the lead position. In a real world large plant environment, fire
water supply isn't always 100% static for emergency fire protection supply.
You have other demands that might include emergency boiler feed water,
emergency chemical process cooling, fire brigade training, filling high
pressure wash trucks, etc. You plan for this with appropriately sized
jockey/booster pump(s), permitting processes, and system monitoring.
However, sometimes, while plant personnel are trying their best to control
these other demands, it is not an exact science and you can start the first
fire pump. These pumps can be at remote locations within the plant and if
you're looking at diesel drive with manual stop, you increase the risk of
that pump starting and operating unattended for not an insignficant period
of time, which with a diesel, can be a real risk. Electric drive takes most
of that away. Add remote start and stop and you have good control and plant
personnel aren't spending their time driving all over the site, chasing an
inadvertent fire pump start.

Hope that helps. Let us know what you end up with for a design.

Richard Malek
[EMAIL PROTECTED]


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Reza
Esmaeili
Sent: Tuesday, September 04, 2007 8:14 AM
To: [email protected]
Subject: RE: Fire Pump Selection - REVISED


Thanks Rechard, you are great!
  As a NFPA member I have asked this question from NFPA-20, I think they
will answer in couple of days, I will attach their answer here. I agree with
you over item 3-3 which is not reasonable, so you mean if I am even less
than 1% unsure about reliability of power source, I am not allowed to use
electric pumps (as main without reserved diesel) and should use diesel
pumps, right? From your experience, would you please let me know in what
kind of industries (May be powerplants,...) or situations we can be sure of
100% reliability of power source to use only electric driven pumps as main?
  Thanks in advance,
  Reza

Richard Malek <[EMAIL PROTECTED]> wrote:



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Reza
Esmaeili
Sent: Tuesday, September 04, 2007 3:28 AM
To: [email protected]
Subject: RE: Fire Pump Selection - REVISED


Richard,
Many thanks for your great explanation. I think my previous question about
selecting of fire pumps was a bit confusing, so I revised it as below.
- Actually this is for a big deluge system, not sprinkler system, I
mistyped sprinkler system in my previous email.
Let me ask my question in another way. I want to asume 3 scenarios for
selecting fire pumps for a water demand of 3900 GPM at 90 Psi.
1- Want to be economical and and I don't afford to buy reserve pumps: (is
it allowed as per NFPA not to have reserve pumps)?
If you are referring to basic NFPA 13, 15, 20, etc. requirements, a reserve
pump isn't required although if you have an electric drive without a
reliable power source, maybe in that case you could say you need a reserve
(i.e. diesel drive) although I wouldn't look at that way. One supply (water
supply + pump in this case) is required and satisfy with diesel or electric.
I'm not sure if there is an occupancy type NFPA standard that requires a
reserve pump (I would doubt it, but I'm not familiar with every NFPA
occupancy type standard)
1-1: I have a very reliable power source: I will buy only an electric
driven main fire pump 3500GPM at 102 psi working at about 112% of rated
capasity ( I won't buy diesel, because I have a reliable power source and
also I want to be economical)
1-2:I doN't have a reliable power source: I will buy only a diesel fire
pump 3500GPM at 102 psi to work as my main fire pump.
1-1/1-2 sound OK


2- have too much money, I will buy reserve pumps:
2-1: I will buy a main electric pump 3500GPM at 102 psi and a diesel pump
3500GPM at 102 psi and my eletric fire pump would be main pump and diesel
pump would be reserve pump which will work at power failure conditions.
2-2: is above arrangement as per NFPA? or I should arrange diesel pump as
main? Either is OK per NFPA from my perspective. If you're only concerned
about power failure, the diesel drive addresses that and the electric would
be unnecessary (diesel is your main AND reserve). If you are looking at
reliability more broadly, an electric paired with a diesel probably provides
some increase in reliability (diesel addesses power availability and
electric addresses the some of the inherent complexity in the diesel drive)

3- Want to be very very economical: I don't want to buy expensive pumps
like Pattreson, Peerless, ... who are producing big pumps, I want to be very
economical and buy the cheap pumps from my supplier who can't make a 3500
GPM pump, so I have to split the pumps and buy two sets of 1500 GPM at 129
psi working at about 130% or rated capacity.
3-1: I have a very reliable power source: I will buy 2 electric pumps each
1500 GPM at 129 psi working as main pumps. Sounds OK, nothing stops you from
using 2 50% pumps in my opinion.
3-2: I doN't have a reliable power source: I will buy 2 diesel pumps each
1500 GPM at 129 psi working as main pumps. Sound OK,

3-3: I am not 100% sure about reliability of power source: I will buy one
electric pumps and one diesel pump at the same capacity of 1500 GPM at 129
psi, electric pump will start first and when water demand exceeds than 1500
GPM, then diesel pump will start, this arrangement is because in case of
power failure, I can supply at least 50% of water demand to control half of
fire. I know this is not logical, but imagine that power failure possibility
is less than 1%. Wouldn't agree with your logic here. 50% supply for a
deluge system isn't of much use. Particularly with the deluge systems, have
to meet or exceed the demand or the protection isn't there.

Regarding the 2 pumps, if you're demand is down to 3900 gpm, you could
likely make that work with a single 3000 gpm. That's nothing that
extraordinary. I would be looking at my estimates for installed cost and
life cycle costs as well for a single vs. 2 pumps. I thnk typically the
owner would be better off with a single 100% pump vs. 2-50%. Good luck.


Would you kindly please analyze these three scenarios and let me know if
any of them is aganist NFPA? If you have to choose one economical choice
(among item 1) and one non economical choice (among item 2), and one very
economical choice (among item 3), which ones you will choose?

Many thanks for your kind help in advance.
Thank,
Reza


---------------------------------
Sick sense of humor? Visit Yahoo! TV's Comedy with an Edge to see what's on,
when.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



---------------------------------
Boardwalk for $500? In 2007? Ha!
Play Monopoly Here and Now (it's updated for today's economy) at Yahoo!
Games.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



---------------------------------
Ready for the edge of your seat? Check out tonight's top picks on Yahoo! TV.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to