How does 5.19.3.4 play into this? It mentions pump discharge piping only...


R/

Matt


Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Wednesday, September 19, 2007 2:58 PM
----- >To: [email protected]
----- >Subject: RE: pump test header location
----- >
----- >My one concern with the arrangement that would flow 
----- >through a system is that the test would occur while the 
----- >building was occupied and if there was a failure what 
----- >the consequences could be.  Granted it wouldn't be 
----- >desirable for it to fail in a fire scenario either.  
----- >
----- >Sorry but I just can't see any reason to put it at the 
----- >end of some bulk main instead of right at the pump.  
----- >
----- >Craig L. Prahl, CET
----- >Fire Protection Group
----- >Mechanical Department
----- >CH2MHILL
----- >Lockwood Greene
----- >1500 International Drive
----- >PO Box 491, Spartanburg, SC  29304-0491
----- >Direct - 864.599.4102
----- >Fax - 864.599.8439
----- >[EMAIL PROTECTED]
----- >http://www.lg.com
----- >
----- >
----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Ed Kramer
----- >Sent: Wednesday, September 19, 2007 3:51 PM
----- >To: [email protected]
----- >Subject: RE: pump test header location
----- >
----- >In this scenario, yes.  I've never considered attaching 
----- >the test header to anyplace other than between the pump 
----- >check and shutoff valve, but it seems it may be common 
----- >practice in some areas.  
----- >
----- >My knee-jerk reaction to pressuring the ENTIRE fire 
----- >protection system when testing a fire pump is that's its 
----- >unwise.  But what's the worst that's going to happen?  
----- >The entire system will see pressures in the ball park of
----- >5 psi greater than the jockey pump pressure (but 
----- >significantly higher when water hammer or pressure waves 
----- >are a factor) and weak pipe/fittings may blow out 
----- >(possibly causing extensive damage) and require 
----- >repair/replacement.  Seems to me it's wiser to find & 
----- >fix weak parts of the system during routine testing than 
----- >it is to find them during a fire emergency.
----- >
----- >Having said that, I still prefer the test header be tied 
----- >in between the pump check & shutoff valve.  Makes for a 
----- >tidy pump package and gives the testing technician the 
----- >option of pressuring the entire system or not.
----- >
----- >Ed Kramer
----- >Littleton, CO
----- >
----- >
----- >>So you'd be flowing through the underground and 
----- >whatever sprinkler 
----- >>system piping just to test a pump?
----- >>
----- >>Craig L. Prahl, CET
----- >>Fire Protection Group
----- >>Mechanical Department
----- >>CH2MHILL
----- >>Lockwood Greene
----- >>1500 International Drive
----- >>PO Box 491, Spartanburg, SC  29304-0491 Direct - 
----- >864.599.4102 Fax -
----- >>864.599.8439 [EMAIL PROTECTED] http://www.lg.com
----- >
----- >>Ron,
----- >>
----- >>Lets say you got a pump that requires 8" discharge 
----- >pipe, your sprinkler
----- >
----- >>bulk main is 6", and you decide to connect the test 
----- >header to the end 
----- >>of the bulk main.  Have you had any problems getting 
----- >the test header 
----- >>calc to work? (never, rarely, sometimes, etc.)
----- >>
----- >>Ed Kramer
----- >>Littleton, CO
----- >>
----- >>
----- >>>It's more common to take the test header off the end 
----- >of bulk main or 
----- >>>combine it with the FDC line if the header is remote 
----- >from the pump
----- >>room.
----- >>>
----- >>>Ron Fletcher
----- >>>Aero Automatic
----- >>>Phoenix, AZ
----- >
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field) 
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to