Thanks Ed, I was fumbling through trying to write
something. It wasn't sounding too coherent.
At 06:36 PM 9/19/2007, you wrote:
Matt & Cliff,
I tend to be a bit picky about definitions being formal and requirements
being spelled out in black & white. It makes for easy interpretation and a
high probability that various professionals will reach the same
interpretation.
You've convinced me that the intent of ". . connection to the pump
discharge pipe . ." in section 5.19.3.4 does mean somewhere between the
pump discharge flange and the shutoff valve. I'm going to submit a
proposal for the next revision. Then it'll be even more black & white.
Ed Kramer
Littleton, CO
>Humm, I see 5.15.1 as a clear definition. The heading 5.15 states
>"Discharge
>Pipe and fittings". So they all have to fall between the discharge flange
>to
>the system side of the discharge valve, pipe included.
>
> If this were not the case, I could make you size all piping downstream of
>a
>1000 gpm pump to 6", even if your crossmain calcs for light hazard
>indicate
>2½"
>
>R/
>
>Matt
>
>Matthew J. Willis
>Living Water Fire Protection, LLC.
>1160 McKenzie Rd.
>PO Box 877
>Cantonment, FL. 32533
>850-937-1850 Voice
>850-937-1852 Facsimile
>[EMAIL PROTECTED]
>
>
>----- >-----Original Message-----
>----- >From: [EMAIL PROTECTED]
>----- >[mailto:[EMAIL PROTECTED] On
>----- >Behalf Of Ed Kramer
>----- >Sent: Wednesday, September 19, 2007 3:46 PM
>----- >To: [email protected]
>----- >Subject: RE: pump test header location
>----- >
>----- >Good point. But I don't see where "discharge pipe" is
>----- >defined anywhere.
>----- >Section 5.15.1 hints at a definition, but doesn't quite
>----- >get there. Without a formal definition, anything
>----- >downstream of the pump could be considered discharge pipe.
>----- >
>----- >Ed Kramer
>----- >Littleton, CO
>----- >
>----- >
>----- >
>----- >>How does 5.19.3.4 play into this? It mentions pump
>----- >discharge piping
>----- >>only...
>----- >>
>----- >>
>----- >>R/
>----- >>
>----- >>Matt
>----- >>
>----- >>
>----- >>Matthew J. Willis
>----- >>Living Water Fire Protection, LLC.
>----- >>1160 McKenzie Rd.
>----- >>PO Box 877
>----- >>Cantonment, FL. 32533
>----- >>850-937-1850 Voice
>----- >>850-937-1852 Facsimile
>----- >>[EMAIL PROTECTED]
>----- >
>----- >
>----- >_______________________________________________
>----- >Sprinklerforum mailing list
>----- >[email protected]
>----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>----- >
>----- >To Unsubscribe, send an email
>----- >to:[EMAIL PROTECTED]
>----- >(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)