Humm, I see 5.15.1 as a clear definition. The heading 5.15 states "Discharge
Pipe and fittings". So they all have to fall between the discharge flange to
the system side of the discharge valve, pipe included.

 If this were not the case, I could make you size all piping downstream of a
1000 gpm pump to 6", even if your crossmain calcs for light hazard indicate
2½"

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Ed Kramer
----- >Sent: Wednesday, September 19, 2007 3:46 PM
----- >To: [email protected]
----- >Subject: RE: pump test header location
----- >
----- >Good point.  But I don't see where "discharge pipe" is 
----- >defined anywhere.
----- >Section 5.15.1 hints at a definition, but doesn't quite 
----- >get there.  Without a formal definition, anything 
----- >downstream of the pump could be considered discharge pipe.
----- >
----- >Ed Kramer
----- >Littleton, CO
----- >
----- > 
----- >
----- >>How does 5.19.3.4 play into this? It mentions pump 
----- >discharge piping 
----- >>only...
----- >>
----- >>
----- >>R/
----- >>
----- >>Matt
----- >>
----- >>
----- >>Matthew J. Willis
----- >>Living Water Fire Protection, LLC.
----- >>1160 McKenzie Rd.
----- >>PO Box 877
----- >>Cantonment, FL. 32533
----- >>850-937-1850 Voice
----- >>850-937-1852 Facsimile
----- >>[EMAIL PROTECTED]
----- >
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to