Matt & Cliff, I tend to be a bit picky about definitions being formal and requirements being spelled out in black & white. It makes for easy interpretation and a high probability that various professionals will reach the same interpretation.
You've convinced me that the intent of ". . connection to the pump discharge pipe . ." in section 5.19.3.4 does mean somewhere between the pump discharge flange and the shutoff valve. I'm going to submit a proposal for the next revision. Then it'll be even more black & white. Ed Kramer Littleton, CO >Humm, I see 5.15.1 as a clear definition. The heading 5.15 states >"Discharge >Pipe and fittings". So they all have to fall between the discharge flange >to >the system side of the discharge valve, pipe included. > > If this were not the case, I could make you size all piping downstream of >a >1000 gpm pump to 6", even if your crossmain calcs for light hazard >indicate >2½" > >R/ > >Matt > >Matthew J. Willis >Living Water Fire Protection, LLC. >1160 McKenzie Rd. >PO Box 877 >Cantonment, FL. 32533 >850-937-1850 Voice >850-937-1852 Facsimile >[EMAIL PROTECTED] > > >----- >-----Original Message----- >----- >From: [EMAIL PROTECTED] >----- >[mailto:[EMAIL PROTECTED] On >----- >Behalf Of Ed Kramer >----- >Sent: Wednesday, September 19, 2007 3:46 PM >----- >To: [email protected] >----- >Subject: RE: pump test header location >----- > >----- >Good point. But I don't see where "discharge pipe" is >----- >defined anywhere. >----- >Section 5.15.1 hints at a definition, but doesn't quite >----- >get there. Without a formal definition, anything >----- >downstream of the pump could be considered discharge pipe. >----- > >----- >Ed Kramer >----- >Littleton, CO >----- > >----- > >----- > >----- >>How does 5.19.3.4 play into this? It mentions pump >----- >discharge piping >----- >>only... >----- >> >----- >> >----- >>R/ >----- >> >----- >>Matt >----- >> >----- >> >----- >>Matthew J. Willis >----- >>Living Water Fire Protection, LLC. >----- >>1160 McKenzie Rd. >----- >>PO Box 877 >----- >>Cantonment, FL. 32533 >----- >>850-937-1850 Voice >----- >>850-937-1852 Facsimile >----- >>[EMAIL PROTECTED] >----- > >----- > >----- >_______________________________________________ >----- >Sprinklerforum mailing list >----- >[email protected] >----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >----- > >----- >To Unsubscribe, send an email >----- >to:[EMAIL PROTECTED] >----- >(Put the word unsubscribe in the subject field) > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > >To Unsubscribe, send an email to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)