Guess we're lucky round here, if it works it's okay. Sometimes we have to calc 
the line between the pump and the header but it always works and is always 
pointless. Measure the flow at the header and pressure at the pump so friction 
loss doesn't matter.

Ever have a diesel pump with 80 ft. of exhaust pipe? How many pipe sizes do you 
increase for distance?

Ron Fletcher
Aero Automatic
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Wednesday, September 19, 2007 4:47 PM
To: [email protected]
Subject: RE: pump test header location

Couple things hit me-
If your piping to the test header is over 15', don't you have to up it a pipe 
size?
Got caught on this once by an arrogant FPE in an $800 trench coat. Don't want 
that to happen again.
So if you're running the pump test header thru a crossmain, you'd have to 
confirm your delivery of the 150% of capacity, not just size the CM for the 
spkr demand.

Interestingly, I don't recall any requirements added for sizing of the UG or 
yard hydrants, or roof hydrant, if they are employed instead.
And allowing these to be used sort of drops any sign of an intent by the 
committee to be emphasizing the test header should be in the pumproom.
The language makes me think it has to work and do what we intended it to do- 
enable us to flow the pump discharge and measure it.

BTW, wouldn't the systems be hamered by the weekly test run anyway? 
Does any one even go out to the pump room and do this manually, and WATCH THE 
PUMP as it does its run, and close then re-open the pump discharge valve?

One of our customers has lost a couple of diesels during weekly test runs. 
Their corp policy is now to do it manually, and operator must monitor the 
engine for overheating, etc.
In our most recent 2500 for them (that's gpm, not how many pumps)we put a 
horn/strobe outside the pump room door to alert any engine trouble signals- 
Since we know that's where the maint guy will be standing, having a smoke.
Ought to scare the heck outa him, eh?

George Church
Rowe Sprinkler
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew J.
Willis
Sent: Wednesday, September 19, 2007 5:03 PM
To: [email protected]
Subject: RE: pump test header location

Humm, I see 5.15.1 as a clear definition. The heading 5.15 states "Discharge 
Pipe and fittings". So they all have to fall between the discharge flange to 
the system side of the discharge valve, pipe included.

 If this were not the case, I could make you size all piping downstream of a 
1000 gpm pump to 6", even if your crossmain calcs for light hazard indicate 2½"

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On
----- >Behalf Of Ed Kramer
----- >Sent: Wednesday, September 19, 2007 3:46 PM
----- >To: [email protected]
----- >Subject: RE: pump test header location
----- >
----- >Good point.  But I don't see where "discharge pipe" is
----- >defined anywhere.
----- >Section 5.15.1 hints at a definition, but doesn't quite
----- >get there.  Without a formal definition, anything
----- >downstream of the pump could be considered discharge pipe.
----- >
----- >Ed Kramer
----- >Littleton, CO
----- >
----- >
----- >
----- >>How does 5.19.3.4 play into this? It mentions pump
----- >discharge piping
----- >>only...
----- >>
----- >>
----- >>R/
----- >>
----- >>Matt
----- >>
----- >>
----- >>Matthew J. Willis
----- >>Living Water Fire Protection, LLC.
----- >>1160 McKenzie Rd.
----- >>PO Box 877
----- >>Cantonment, FL. 32533
----- >>850-937-1850 Voice
----- >>850-937-1852 Facsimile
----- >>[EMAIL PROTECTED]
----- >
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to