You have to look at each project independently.  When you're
constructing a $300-500 million dollar manufacturing facility, spending
$5000 on guard shack sprinklers is not usually even looked at.  If
you're adding sprinklers to the guard shack at the local condominium
then you would look at things in a different light because $5000 would
cause someone to have a stroke.  

There's no boiler plate solution that fits every project, but there's
also no need to over complicate things either.  


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Thursday, October 04, 2007 5:24 PM
To: [email protected]
Subject: RE: Underground Material

Of course that's true, but what you're describing is insanity carried
out to two decimal places.   I think Thom McMahon's earlier comment,
which may not have been understood as tongue-in-cheek, was more profound
than he's getting credit for.  Yes, you have an existing yard system of
larger ferrous piping, so why not just install the 4" ductile and be
done with it?  Well, one reason is that it's ridiculously expensive
compared to the alternatives (Thom's point) and the alternatives will
serve the application well.   

I see two really important and salient points here:  1) That the owner's
money is as important to them as ours is to us and even if they could
afford it, why drive the cost of fire protection up unnecessarily?
What's the number one objection to fire sprinklers?  Cost.  How can we
enhance the chance to put sprinklers into every new building (and as
many existing as possible)?   Manage costs, among other things.  And
this applies just as certainly to commercial/industrial as to
residential - just ask the families of firefighters and the owners of
the Sofa Super Store in Charleston, SC (thanks Thom).   2) As Gregg's
story attests to, if you give some AHJ's an inch they'll take a mile.
One reason that I choose to challenge certain AHJ rulings or
interpretations that I many not agree with from time to time is because
I have other clients and other (future) projects for which I don't want
today's insanity to become a precedent for tomorrow's.   Our community,
including and especially the project owner, is owed a certain
cost-benefit for her or his expenditure and my role as a consultant to
uphold applicable codes and standards, but also to advocate for my
client so that they're not running 4" underground to an outhouse.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg
Fontes
Sent: Thursday, October 04, 2007 2:11 PM
To: [email protected]
Subject: RE: Underground Material

We can relate to this.  We have a couple of jurisdictions here in the
Central Valley that require fire sprinklers in all commercial structures
regardless of sq. ft.  We too have had to sprinkle 5' X 5' guard shacks
with 4" underground and fully equipped fire sprinkler riser with flow
switch and
bell.  It pays to know the jurisdiction in which you work.   

Gregg Fontes
Cen-Cal Fire Systems, Inc.
(209)334-9119

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- FPDC
Sent: Thursday, October 04, 2007 1:58 PM
To: [email protected]
Subject: Re: Underground Material

First, why are sprinklers required in the Guard Shacks? I would think
that per Section 904 of the MA Code, sprinklers could be omitted. If
this is an Insurance Company or similar requirement, they should be able
to give you guidance. Secondly, this does fall under Limited Area
Sprinkler System because of the definition in the Code. Third, are there
domestic connections for the guard shacks? If so, why can't sprinklers
be installed per the section in 101 where up to 6 sprinklers may be fed
off the domestic? This might be a good situation to invoke that. Fourth,
have you checked with the water purveyor? (assuming this is a boosted
public supply) They may have restrictions on what type of pipe may be
connected.


At 09:23 AM 10/4/2007, you wrote:
>We have a situation where we need to put sprinklers in the guardhouses
at
>the entrances to a larger manufacturing facility. The one guardhouse
will
>have 6 heads and the other 4. We would like to supply the buildings
with 2"
>underground. With the exception of copper what are my choices for an 
>approved 2" underground pipe material? The project is located in MA.
>
>Matthew Drewello, PE
>
>Fluor Corporation
>100 Fluor Daniel Drive
>Greenville, SC 29607
>------------------------------------------------------------
>The information transmitted is intended only for the person or entity 
>to which it is addressed and may contain proprietary, 
>business-confidential and/or privileged material.
>If you are not the intended recipient of this message you are hereby 
>notified that any use, review, retransmission, dissemination, 
>distribution, reproduction or any action taken in reliance upon this 
>message is prohibited. If you received this in error, please contact 
>the sender and delete the material from any computer.
>
>Any views expressed in this message are those of the individual sender 
>and may not necessarily reflect the views of the company.
>------------------------------------------------------------
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to