On another subject, excellent AFSA bulletin on grounding and bonding
sprinkler piping. This is an area that even electrical contractors have
trouble with. As the article notes its imperative that bonding and grounding
be distinguished. The difference is significant. While using sprinkler
piping as a grounding electrode is prohibited, bonding metallic sprinkler
piping is mandatory pursuant to the National Electrical Code.

Unfortunately I still find bonding connections being removed by misinformed
sprinkler personnel. This action not only is a violation of the electrical
contractors act and the NEC but actually increases the risk of electrocution
to sprinkler fitters and inspection personnel. Without the bonding
connection to the buildings electrical service it is entirely possible,
especially in wooden structures, that sprinkler piping can become energized.
It could be as simple as an open 277 volt lighting circuit laying across a
section of 1" black steel. The mechanic who makes the connection to ground
or another bonded object completes the circuit risking injury or death. 

So for the sake of sprinkler personnel make sure all metallic sprinkler
piping is properly bonded by the electrical contractor. As a matter of fact
the next time you cant find the bonding connection ask why and insist that
it be made for your own safety.

Great Job AFSA.

Sincerely,

John Drucker
Fire Protection Subcode Official
Licensed Electrical Contractor
New Jersey
 