First, why are sprinklers required in the Guard Shacks? I would think
that per Section 904 of the MA Code, sprinklers could be omitted. If
this is an Insurance Company or similar requirement, they should be
able to give you guidance. Secondly, this does fall under Limited
Area Sprinkler System because of the definition in the Code. Third,
are there domestic connections for the guard shacks? If so, why can't
sprinklers be installed per the section in 101 where up to 6
sprinklers may be fed off the domestic? This might be a good
situation to invoke that. Fourth, have you checked with the water
purveyor? (assuming this is a boosted public supply) They may have
restrictions on what type of pipe may be connected.
At 09:23 AM 10/4/2007, you wrote:
We have a situation where we need to put sprinklers in the guardhouses at
the entrances to a larger manufacturing facility. The one guardhouse will
have 6 heads and the other 4. We would like to supply the buildings with 2"
underground. With the exception of copper what are my choices for an
approved 2" underground pipe material? The project is located in MA.
Matthew Drewello, PE
Fluor Corporation
100 Fluor Daniel Drive
Greenville, SC 29607
------------------------------------------------------------
The information transmitted is intended only for the person
or entity to which it is addressed and may contain
proprietary, business-confidential and/or privileged material.
If you are not the intended recipient of this message you are
hereby notified that any use, review, retransmission, dissemination,
distribution, reproduction or any action taken in reliance upon
this message is prohibited. If you received this in error, please
contact the sender and delete the material from any computer.
Any views expressed in this message are those of the individual
sender and may not necessarily reflect the views of the company.
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)