We can relate to this.  We have a couple of jurisdictions here in the
Central Valley that require fire sprinklers in all commercial structures
regardless of sq. ft.  We too have had to sprinkle 5' X 5' guard shacks with
4" underground and fully equipped fire sprinkler riser with flow switch and
bell.  It pays to know the jurisdiction in which you work.   

Gregg Fontes
Cen-Cal Fire Systems, Inc.
(209)334-9119

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Thursday, October 04, 2007 1:58 PM
To: [email protected]
Subject: Re: Underground Material

First, why are sprinklers required in the Guard Shacks? I would think 
that per Section 904 of the MA Code, sprinklers could be omitted. If 
this is an Insurance Company or similar requirement, they should be 
able to give you guidance. Secondly, this does fall under Limited 
Area Sprinkler System because of the definition in the Code. Third, 
are there domestic connections for the guard shacks? If so, why can't 
sprinklers be installed per the section in 101 where up to 6 
sprinklers may be fed off the domestic? This might be a good 
situation to invoke that. Fourth, have you checked with the water 
purveyor? (assuming this is a boosted public supply) They may have 
restrictions on what type of pipe may be connected.


At 09:23 AM 10/4/2007, you wrote:
>We have a situation where we need to put sprinklers in the guardhouses at
>the entrances to a larger manufacturing facility. The one guardhouse will
>have 6 heads and the other 4. We would like to supply the buildings with 2"
>underground. With the exception of copper what are my choices for an
>approved 2" underground pipe material? The project is located in MA.
>
>Matthew Drewello, PE
>
>Fluor Corporation
>100 Fluor Daniel Drive
>Greenville, SC 29607
>------------------------------------------------------------
>The information transmitted is intended only for the person
>or entity to which it is addressed and may contain
>proprietary, business-confidential and/or privileged material.
>If you are not the intended recipient of this message you are
>hereby notified that any use, review, retransmission, dissemination,
>distribution, reproduction or any action taken in reliance upon
>this message is prohibited. If you received this in error, please
>contact the sender and delete the material from any computer.
>
>Any views expressed in this message are those of the individual
>sender and may not necessarily reflect the views of the company.
>------------------------------------------------------------
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to