I asked this question in writing from Tyco and Reliable, long, long time ago. Reliable never got back to me. Each time I questioned, they said they would get back to me. Tyco, replied to me, that the soffit on the wall across from the sprinkler head was an obstruction. When I asked for it in writing, they refused, saying it is an obstruction as per NFPA.
Tony -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight Sent: October 29, 2007 1:31 PM To: [email protected] Subject: RE: Residental Sidewall Soffit Obstruction Rich, If this were my design I would not place a second sprinkler in a soffit that is across the room and against the wall. The purpose of RES sprinklers in part is to wet the walls, right? Draw yourself a side view elevation and using common sense and good judgment, how much wall wetting will be inhibited by the soffit. In my estimation, the amount would be negligible, and therefore an additional sprinkler would not be necessary. In this instance, the obstruction will not impede heat flow, nor have an appreciable impact on discharge. If the obstruction were in the middle of the room the story would be different since the pattern would be substantially impacted. Letter of the law says yes, but the gray area using good judgment says no. Just my opinion based on nothing other then that, Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of R Richardson Sent: Monday, October 29, 2007 11:41 AM To: [email protected] Subject: Residental Sidewall Soffit Obstruction Is the intent of NFPA 13 to treat a soffit on the opposite wall from which a residential sprinkler head is installed as a beam with respect to obstruction to spray pattern? Or can one ignore the area under the soffitt. The case we have is a 1 ft. deep soffit along the wall opposite from the wall where the residential sidewall head is mounted. A straight NFPA 13 application sends one to the beam rule, which requires the head to head to be at least 14 ft. away, but it is only 10 ft. away. So does one really have to install a head under the 1 x 1 ft. soffit on the opposite side of the room where the sidewall head is located? Note: 2007 NFPA 13 section 8.7.5.1.5 for standard sidewall heads has an allowance to ignore the soffit on the opposite wall, but this is the only place we can find this situation addressed. Thanks, Rich Richardson Seattle Fire Department _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: 10/28/2007 1:58 PM No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: 10/28/2007 1:58 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)