I asked this question in writing from Tyco and Reliable, long, long time
ago. Reliable never got back to me. Each time I questioned, they said they
would get back to me. Tyco, replied to me, that the soffit on the wall
across from the sprinkler head was an obstruction. When I asked for it in
writing, they refused, saying it is an obstruction as per NFPA.

Tony  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: October 29, 2007 1:31 PM
To: [email protected]
Subject: RE: Residental Sidewall Soffit Obstruction

Rich,
If this were my design I would not place a second sprinkler in a soffit that
is across the room and against the wall.  The purpose of RES sprinklers in
part is to wet the walls, right?  Draw yourself a side view elevation and
using common sense and good judgment, how much wall wetting will be
inhibited by the soffit.  In my estimation, the amount would be negligible,
and therefore an additional sprinkler would not be necessary.  In this
instance, the obstruction will not impede heat flow, nor have an appreciable
impact on discharge.  If the obstruction were in the middle of the room the
story would be different since the pattern would be substantially impacted.
Letter of the law says yes, but the gray area using good judgment says no.

Just my opinion based on nothing other then that,

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of R Richardson
Sent: Monday, October 29, 2007 11:41 AM
To: [email protected]
Subject: Residental Sidewall Soffit Obstruction

Is the intent of NFPA 13 to treat a soffit on the opposite wall from which a
residential sprinkler head is installed as a beam with respect to
obstruction to spray pattern?  Or can one ignore the area under the soffitt.

The case we have is a 1 ft. deep soffit along the wall opposite from the
wall where the residential sidewall head is mounted.   A straight NFPA 13
application sends one to the beam rule, which requires the head to head to
be at least 14 ft. away, but it is only 10 ft. away.  So does one really
have to install a head under the 1 x 1 ft. soffit on the opposite side of
the room where the sidewall head is located?

Note: 2007 NFPA 13 section 8.7.5.1.5  for standard sidewall heads has an
allowance to ignore the soffit on the opposite wall, but this is the only
place we can find this situation addressed.

Thanks,

Rich Richardson
Seattle Fire Department

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: 10/28/2007
1:58 PM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: 10/28/2007
1:58 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to