Dan, As I understand it and apply it, the pump curves (and therefore churn pressure, etc.) are established by correcting back to rated speed. There is going to be some diesel droop or motor slip, so as Frans indicates with NFPA 20, when you're engine is set to operate at rated speed at max load, you're going to see higher RPM and therefore higher churn pressures than what is published by the pump manufacturer.
FM Approval standard states +/- 10% RPM of rated is acceptable, however, the NFPA 20 criteria seems like the more definitive requirement - meet rated speed at max load and not greater than 10% additional at churn. If you're not meeting rated speed requirement at 150%, that's a problem per 20. However, 20 allows that 10% difference between churn and max load. When I have had to get this tight on churn, the diesel engine manufacturers will provide guidance on how much droop to account for which has been in the 4-5% range. I don't think 20, etc. are that clear on the droop issue. Most of the time I think it is just taken as pump manufacturers published churn pressure, which is corrected back to rated RPM. Depending on driver and specific manufacturer/model data, there would be some variability and difficulty in a pump manufacturer developing "driven" churn pressures. That's where the engineer/designer has to integrate the driver and pump under actual operating conditions to determining system pressure characteristics, etc. Rich Richard Malek [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of danarbel Sent: Tuesday, October 30, 2007 3:20 AM To: [email protected] Subject: Fire Pump performance as per the name plate Dear All, I have got a problem with a fire pump. The pump performance does not match the name plant data. The cause is the Diesel Engine. The engine RPM deviation from "No Load" to 150% nominal is 90 rpm, just over 5% of the nominal (1760 rpm). The result is too high pressure (5% excess) at churning causing operation of the 175psi relief valves of the sprinkler systems, At the other end, 150% flow, the pressure is 5% below the name plant data. The question: To what extent the pump supplier is bound by the name plant performance data. The supplier Rep. argues that 5% deviation is within the normal. Dan Arbel Tel: 972-4-8243337 Fax: 972-4-8243278 M: 972-52-2810593 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)