I read the question wrong and thought this was NOT a 13 application. Since it is 13 I retract all I said and agree that soffit rules DO apply. I also agree that the dimension is from the plane of the deflector and so if the sidewall were sufficiently dropped (within the listing of course) then the twelve inch soffit essentially becomes eight or six or zero inch soffit. As example if you were to use the twelve inch maximum listed sidewall the soffit on the opposite wall would cease to exist as an obstruction at all.
On 10/30/07, Thom McMahon <[EMAIL PROTECTED]> wrote: > They are an obstruction as per NFPA 13, 2007 8.10.7.1.3 This section is for > the installation of residential sidewall sprinklers. You should not rely on > 13R or 13D when you are in a 13 application, especially when 13 clearly > spells out what is an obstruction and how to deal with it. > > >From my previous post: > > There are listed residential HSW sprinkler heads that can be mounted 12" > down from the ceiling. if these heads are installed there would not be an > issue with a soffitt that is only 12 " deep on the opposite wall. > If you are using any other placement location for the HSW then you will have > to meet the rules of Table 8.10.7.1.3 "Positioning of sprinklers to avoid > obstructions (residential sidewall sprinklers) This is as directed > 8.10.7.1.3 for obstructions more than 8'-0" from the sprinkler----. > > Thom McMahon > Firetech, Inc. > 2560 Copper Ridge Dr > Steamboat Springs, CO 80488-2136 > Tel: 970-879-7952 > Fax: 970-879-7926 > ----- Original Message ----- > From: "A.P.Silva" <[EMAIL PROTECTED]> > To: <[email protected]> > Sent: Monday, October 29, 2007 10:54 PM > Subject: RE: Residental Sidewall Soffit Obstruction > > > >I asked this question in writing from Tyco and Reliable, long, long time > > ago. Reliable never got back to me. Each time I questioned, they said they > > would get back to me. Tyco, replied to me, that the soffit on the wall > > across from the sprinkler head was an obstruction. When I asked for it in > > writing, they refused, saying it is an obstruction as per NFPA. > > > > Tony > > > > -----Original Message----- > > From: [EMAIL PROTECTED] > > [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight > > Sent: October 29, 2007 1:31 PM > > To: [email protected] > > Subject: RE: Residental Sidewall Soffit Obstruction > > > > Rich, > > If this were my design I would not place a second sprinkler in a soffit > > that > > is across the room and against the wall. The purpose of RES sprinklers in > > part is to wet the walls, right? Draw yourself a side view elevation and > > using common sense and good judgment, how much wall wetting will be > > inhibited by the soffit. In my estimation, the amount would be > > negligible, > > and therefore an additional sprinkler would not be necessary. In this > > instance, the obstruction will not impede heat flow, nor have an > > appreciable > > impact on discharge. If the obstruction were in the middle of the room > > the > > story would be different since the pattern would be substantially > > impacted. > > Letter of the law says yes, but the gray area using good judgment says no. > > > > Just my opinion based on nothing other then that, > > > > Bob Knight > > > > -----Original Message----- > > From: [EMAIL PROTECTED] > > [mailto:[EMAIL PROTECTED] On Behalf Of R > > Richardson > > Sent: Monday, October 29, 2007 11:41 AM > > To: [email protected] > > Subject: Residental Sidewall Soffit Obstruction > > > > Is the intent of NFPA 13 to treat a soffit on the opposite wall from which > > a > > residential sprinkler head is installed as a beam with respect to > > obstruction to spray pattern? Or can one ignore the area under the > > soffitt. > > > > The case we have is a 1 ft. deep soffit along the wall opposite from the > > wall where the residential sidewall head is mounted. A straight NFPA 13 > > application sends one to the beam rule, which requires the head to head to > > be at least 14 ft. away, but it is only 10 ft. away. So does one really > > have to install a head under the 1 x 1 ft. soffit on the opposite side of > > the room where the sidewall head is located? > > > > Note: 2007 NFPA 13 section 8.7.5.1.5 for standard sidewall heads has an > > allowance to ignore the soffit on the opposite wall, but this is the only > > place we can find this situation addressed. > > > > Thanks, > > > > Rich Richardson > > Seattle Fire Department > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > > (Put the word unsubscribe in the subject field) > > > > No virus found in this incoming message. > > Checked by AVG Free Edition. > > Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: > > 10/28/2007 > > 1:58 PM > > > > > > No virus found in this outgoing message. > > Checked by AVG Free Edition. > > Version: 7.5.503 / Virus Database: 269.15.12/1097 - Release Date: > > 10/28/2007 > > 1:58 PM > > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > > (Put the word unsubscribe in the subject field) > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > > (Put the word unsubscribe in the subject field) > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)