Dan asked,
Is the name plate data means min. guarantied performance or is it
meaningless?
It is the flow and pressure obtained at the factory at a final test before
shipping but under precise rated conditions. It may not be obtained during a
field test due to the variables of the field conditions but if adjusted back
to rated it should be there. 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Wednesday, October 31, 2007 11:03 AM
To: [email protected]
Subject: RE: Fire Pump performance as per the name plate

It's called pump affinity and must be done.
Also, when discharge and suction are 2 pipe diameters or greater in size,
velocity calculations should also be applied.  And, I would take your
discharge pressure after the check on the sensing line as you might not get
an actual until the pipe size goes back to supply size.
Tom


Gage readings during a pump test are not the final criteria. The pump speed
must be changed to pump rated speed and the pressure and flow is adjusted
accordingly. The new curve is to meet factory specs.


I am aware of all that.

The 10% engine speed allowance is reflected in 20% pressure range.

I get a pump package from a supplier.


Dan


Dan,

NFPA 20-2007 paragraph 11.2.4.1.1:
"Engines shall be provided with a governor capable of regulating
engine speed within a range of 10 percent between shutoff and maximum
load condition of the pump."

Does this help: paragraph 11.2.4.1.2
"The governor shall be field adjustable and set and secured to
maintain rated pump speed at maximum pump load." ?

The pump in concern should have a pressure relief valve installed per
paragraph 5.18.1.1:
"Where a diesel engine fire pump is installed and where a total of
121 percent of the net rated shutoff (churn) pressure plus the
maximum static suction pressure, adjusted for elevation, exceeds the
pressure for which the system components are rated, a pressure relief
valve shall be installed."

If the water supply has its own storage tank(s), you may be able to
solve the problem by piping the discharge side of this relief valve
back to the water storage tank.

Although, note that paragraph 5.7.4.2 does not allow to use the
relief valve for this purpose:
"Pressure relief valves shall not be used as a means to meet the
requirements of 5.7.4.1."

You may also find other useful text in section 5.7.4* Maximum
Pressure for Centrifugal Pumps.
like paragraph 5.7.4.1:
"The net pump shutoff (churn) pressure plus the maximum static
suction pressure, adjusted for elevation, shall not exceed the
pressure for which the system components are rated."

It says "net pressure" , no 5% allowance mentioned.

Frans Stoop
TOS architecture & fire protection
Netherlands


At 10:20 30-10-2007 +0200, you wrote:

>Dear All,
>
>I have got a problem with a fire pump.
>
>The pump performance does not match the name plant data.
>
>The cause is the Diesel Engine.
>
>The engine RPM deviation from "No Load" to 150% nominal is 90 rpm, just
over
>5% of the nominal (1760 rpm).
>
>The result is too high pressure (5% excess) at churning causing operation
of
>the 175psi relief valves of the sprinkler systems,
>
>At the other end, 150% flow, the pressure is 5% below the name plant data.
>
>The question: To what extent the pump supplier is bound by the name plant
>performance data.
>
>The supplier Rep. argues that 5% deviation is within the normal.
>
>
>Dan Arbel
>Tel: 972-4-8243337
>Fax: 972-4-8243278
>M: 972-52-2810593


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to