Hello Karen,

Wednesday, October 31, 2007, 11:59:41 AM, you wrote:

KP> I need to know if there is a code anywhere that states you can or can not
KP> use a standard pendant head as a window wash. I have a glass wall that I
KP> need to be fire rated and I have a contractor telling me by code he can use
KP> a pendant head instead of a deluge head or a Tyco window sprinkler. The only
KP> code I see that possibly address this is 21.20.1.2.1 and it only says you
KP> have to use automatic heads. Any help!!!!!

If this is an atrium wall, the prescriptive requirements are in IBC
404.

A code-required fire rated wall must have been tested by an approved
agency such as UL.  Two ways to get any-hour rating is with
Fire-protection-rated glazing in the wall or using the Tyco WS
sprinkler which is 2 hour only which obviously qualifies for 1 hour.
But the glass wall MUST follow the construction in the listings.

Here are links to the Tyco information and the ICC-NES report.

http://www.tyco-fire.com/TD_TFP/TFP/TFP620_07_2005.pdf

http://www.icc-es.org/reports/pdf_files/NES/NER516.pdf

-- 
Best regards,

Daniel Kaczor, Plans Examiner

[EMAIL PROTECTED]