We have historically used standard spray sprinklers in order to provide a 1 hr rating with ANY glass partition but technically (at least the last time I did a search) it's only in the code (Life Safety Code for sure) for glass in ATRIUMS. Even then you have the wrinkle of MUST wet the ENTIRE glass surface.

The WS sprinkler can be used where ever in accordance with its listing AND provides an equivalency for up to 2 hr rated construction.

Roland

On Oct 31, 2007, at 9:59 AM, Karen Purvis wrote:

I need to know if there is a code anywhere that states you can or can not use a standard pendant head as a window wash. I have a glass wall that I need to be fire rated and I have a contractor telling me by code he can use a pendant head instead of a deluge head or a Tyco window sprinkler. The only code I see that possibly address this is 21.20.1.2.1 and it only says you
have to use automatic heads. Any help!!!!!