mike,

I don't think you'll find any 13 requirement for low air alarms except
in refrigerated spaces. General low air monitoring is in 72 just like
high air.

On 11/5/07, Mike Brown (TECH- GVL) <[EMAIL PROTECTED]> wrote:
> The monitoring of a high pressure is not in NFPA 13 or any other NFPA
> Pamphlet except in NFPA 72, and the NFPA 13 Committee has never seen fit
> to put it in NFPA 13.  I have never met anyone that could tell me why it
> was in NFPA 72.
> Mike Brown
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ron
> Greenman
> Sent: Wednesday, October 24, 2007 9:58 PM
> To: [email protected]
> Subject: Re: Supervisory Alarm - Low Air
>
> Of course! How foolish of me! Dave, can you send me your address. I
> lost it and I want to send your Tacoma Code Book.
>
> On 10/24/07, David de Vries <[EMAIL PROTECTED]> wrote:
> > How would you know?  Simple, Ron.  You would just check the log where
> the building engineer dutifully recorded the air pressure on the system
> on a weekly basis, as required by NFPA 25 where there is no electrical
> supervison, of course!
> >
> >   lol
> >
> >   Dave at Firetech Engineering Incorp.
> >
> > Ron Greenman <[EMAIL PROTECTED]> wrote:
> >   I've always considered the high air supervision more critical than
> low
> > since a malfunctioning compressor that runs the air up will cause a
> > longer trip time whereas low air will just let you know that an
> > unwanted trip could happen if not attended to. Of course the emphasis
> > is put on the low air because that trip rolls fire trucks, requires a
> > technician to be summoned, disrupts the normal course of a day and
> > costs the owner money. All recordable events and therefore
> > statistically useful for proving one point or another. If, on the
> > other hand, you receive a high air you just fix the problem as a piece
> > of equipment that needs maintenance. If a life or building was ever
> > lost because of high air delaying a trip how would anyone ever know?
> > The evidence would demonstrate an overwhelmed system but although it
> > might suggest it there is nothing I can think of that would
> > definitively demonstrate it was due to a delayed trip time. If a bear
> > ....s in the woods...?
> >
> > On 10/24/07, Tim Frankenberg wrote:
> > > Dave,
> > >
> > > The requirement to monitor low and high air pressure has been in the
> code before the 1993 edition of the National Fire Alarm Code.
> > >
> > > Most of the supervisory pressure switches installed are very much
> capable of monitoring both low and high air and have been able to for
> many, many years. More times than not, the high air condition is not
> being enforced by the AHJ.
> > >
> > > Kind Regards,
> > >
> > > Tim Frankenberg, CFPS
> > >
> > > Tim Frankenberg, CFPS
> > > Fire Product Manager
> > > Potter Electric Signal Company
> > > www.pottersignal.com
> > > 800-325-3936
> > >
> > > >>> "Dave Phelan" 10/23/2007 4:52 PM >>>
> > > Something new to me popped up today as we are now using the 2002
> editions of
> > > 13 & 72 here.
> > >
> > > On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72
> states that
> > > the air supervisory sensor shall signal on loss of 10 PSI but also
> on 10 PSI
> > > greater than the system set pressure. Check out 5.13 for yourself
> but I'm
> > > thinking Ive never seen or tested for air greater than 10 PSI of the
> set
> > > pressure before.
> > >
> > > How is this being handled in the field during installs and
> maintenance ?
> > > Does the typical air pressure switch in the little red cover
> actually cover
> > > both loss and increase pressures?
> > >
> > > Thanks.
> > >
> > > Dave - a NJ AHJ
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> >
> >
> > --
> > Ron Greenman
> > at home....
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman