I don't have a copy of 13 with me however, 13 refers you to 72 under certain 
conditions. As I recall this is in the body of the standard.

Mike Cabral

---- Ron Greenman <[EMAIL PROTECTED]> wrote: 
> mike,
> 
> I don't think you'll find any 13 requirement for low air alarms except
> in refrigerated spaces. General low air monitoring is in 72 just like
> high air.
> 
> On 11/5/07, Mike Brown (TECH- GVL) <[EMAIL PROTECTED]> wrote:
> > The monitoring of a high pressure is not in NFPA 13 or any other NFPA
> > Pamphlet except in NFPA 72, and the NFPA 13 Committee has never seen fit
> > to put it in NFPA 13.  I have never met anyone that could tell me why it
> > was in NFPA 72.
> > Mike Brown
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Ron
> > Greenman
> > Sent: Wednesday, October 24, 2007 9:58 PM
> > To: [email protected]
> > Subject: Re: Supervisory Alarm - Low Air
> >
> > Of course! How foolish of me! Dave, can you send me your address. I
> > lost it and I want to send your Tacoma Code Book.
> >
> > On 10/24/07, David de Vries <[EMAIL PROTECTED]> wrote:
> > > How would you know?  Simple, Ron.  You would just check the log where
> > the building engineer dutifully recorded the air pressure on the system
> > on a weekly basis, as required by NFPA 25 where there is no electrical
> > supervison, of course!
> > >
> > >   lol
> > >
> > >   Dave at Firetech Engineering Incorp.
> > >
> > > Ron Greenman <[EMAIL PROTECTED]> wrote:
> > >   I've always considered the high air supervision more critical than
> > low
> > > since a malfunctioning compressor that runs the air up will cause a
> > > longer trip time whereas low air will just let you know that an
> > > unwanted trip could happen if not attended to. Of course the emphasis
> > > is put on the low air because that trip rolls fire trucks, requires a
> > > technician to be summoned, disrupts the normal course of a day and
> > > costs the owner money. All recordable events and therefore
> > > statistically useful for proving one point or another. If, on the
> > > other hand, you receive a high air you just fix the problem as a piece
> > > of equipment that needs maintenance. If a life or building was ever
> > > lost because of high air delaying a trip how would anyone ever know?
> > > The evidence would demonstrate an overwhelmed system but although it
> > > might suggest it there is nothing I can think of that would
> > > definitively demonstrate it was due to a delayed trip time. If a bear
> > > ....s in the woods...?
> > >
> > > On 10/24/07, Tim Frankenberg wrote:
> > > > Dave,
> > > >
> > > > The requirement to monitor low and high air pressure has been in the
> > code before the 1993 edition of the National Fire Alarm Code.
> > > >
> > > > Most of the supervisory pressure switches installed are very much
> > capable of monitoring both low and high air and have been able to for
> > many, many years. More times than not, the high air condition is not
> > being enforced by the AHJ.
> > > >
> > > > Kind Regards,
> > > >
> > > > Tim Frankenberg, CFPS
> > > >
> > > > Tim Frankenberg, CFPS
> > > > Fire Product Manager
> > > > Potter Electric Signal Company
> > > > www.pottersignal.com
> > > > 800-325-3936
> > > >
> > > > >>> "Dave Phelan" 10/23/2007 4:52 PM >>>
> > > > Something new to me popped up today as we are now using the 2002
> > editions of
> > > > 13 & 72 here.
> > > >
> > > > On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72
> > states that
> > > > the air supervisory sensor shall signal on loss of 10 PSI but also
> > on 10 PSI
> > > > greater than the system set pressure. Check out 5.13 for yourself
> > but I'm
> > > > thinking Ive never seen or tested for air greater than 10 PSI of the
> > set
> > > > pressure before.
> > > >
> > > > How is this being handled in the field during installs and
> > maintenance ?
> > > > Does the typical air pressure switch in the little red cover
> > actually cover
> > > > both loss and increase pressures?
> > > >
> > > > Thanks.
> > > >
> > > > Dave - a NJ AHJ
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > >
> > > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > > (Put the word unsubscribe in the subject field)
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > >
> > > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > > (Put the word unsubscribe in the subject field)
> > > >
> > >
> > >
> > > --
> > > Ron Greenman
> > > at home....
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> >
> >
> > --
> > Ron Greenman
> > at home....
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> 
> 
> -- 
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to