Maybe I'm missing something here, but for the impact to us, it's a double
pole pressure switch on all dry systems, and if Sparky wants or needs to
wire it up, that's a good thing but not my problem?

We install low air switches on all of our dry & Preaction systems - if
nothing else, if there's a false trip and freezeup damage, we've got a
lawsuit.
I can walk into court, point out that the low air switch was furnished and
installed by us- whether or not a code requirement- and its up to others to
wire it so it does something. And had they done that, then the impending
false trip (cause someone threw the breaker to the compressor, or the
compressor crapped out, or whatever) could have been spotted and rectified
when the low air switch went off, so someone should share the cost of this
flood wit my carrier since it could have been prevented, we enabled the
Owner/FA guy, whatever and they didn't take advantage of it.

For $50 it's a cheap insurance policy.

On a related note, we've encountered some real estate management companies
who keep the riser room key remote from the building. We may mention tat our
insrance carrier picks up the first ten minutes of flow damage on a
premature activation- if it runs 5 hours cause you gotta run across town to
get the key to shut and drain, that would be your insurance carrier's
problem. Haven't haad to go to court over that one, and this particular firm
didn't change their SOP when we brought it up. (sigh)

glc  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Cabral
Sent: Wednesday, November 07, 2007 12:54 PM
To: [email protected]
Subject: Re: Supervisory Alarm - Low Air

I don't have a copy of 13 with me however, 13 refers you to 72 under certain
conditions. As I recall this is in the body of the standard.

Mike Cabral

---- Ron Greenman <[EMAIL PROTECTED]> wrote: 
> mike,
> 
> I don't think you'll find any 13 requirement for low air alarms except
> in refrigerated spaces. General low air monitoring is in 72 just like
> high air.
> 
> On 11/5/07, Mike Brown (TECH- GVL) <[EMAIL PROTECTED]> wrote:
> > The monitoring of a high pressure is not in NFPA 13 or any other NFPA
> > Pamphlet except in NFPA 72, and the NFPA 13 Committee has never seen fit
> > to put it in NFPA 13.  I have never met anyone that could tell me why it
> > was in NFPA 72.
> > Mike Brown
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Ron
> > Greenman
> > Sent: Wednesday, October 24, 2007 9:58 PM
> > To: [email protected]
> > Subject: Re: Supervisory Alarm - Low Air
> >
> > Of course! How foolish of me! Dave, can you send me your address. I
> > lost it and I want to send your Tacoma Code Book.
> >
> > On 10/24/07, David de Vries <[EMAIL PROTECTED]> wrote:
> > > How would you know?  Simple, Ron.  You would just check the log where
> > the building engineer dutifully recorded the air pressure on the system
> > on a weekly basis, as required by NFPA 25 where there is no electrical
> > supervison, of course!
> > >
> > >   lol
> > >
> > >   Dave at Firetech Engineering Incorp.
> > >
> > > Ron Greenman <[EMAIL PROTECTED]> wrote:
> > >   I've always considered the high air supervision more critical than
> > low
> > > since a malfunctioning compressor that runs the air up will cause a
> > > longer trip time whereas low air will just let you know that an
> > > unwanted trip could happen if not attended to. Of course the emphasis
> > > is put on the low air because that trip rolls fire trucks, requires a
> > > technician to be summoned, disrupts the normal course of a day and
> > > costs the owner money. All recordable events and therefore
> > > statistically useful for proving one point or another. If, on the
> > > other hand, you receive a high air you just fix the problem as a piece
> > > of equipment that needs maintenance. If a life or building was ever
> > > lost because of high air delaying a trip how would anyone ever know?
> > > The evidence would demonstrate an overwhelmed system but although it
> > > might suggest it there is nothing I can think of that would
> > > definitively demonstrate it was due to a delayed trip time. If a bear
> > > ....s in the woods...?
> > >
> > > On 10/24/07, Tim Frankenberg wrote:
> > > > Dave,
> > > >
> > > > The requirement to monitor low and high air pressure has been in the
> > code before the 1993 edition of the National Fire Alarm Code.
> > > >
> > > > Most of the supervisory pressure switches installed are very much
> > capable of monitoring both low and high air and have been able to for
> > many, many years. More times than not, the high air condition is not
> > being enforced by the AHJ.
> > > >
> > > > Kind Regards,
> > > >
> > > > Tim Frankenberg, CFPS
> > > >
> > > > Tim Frankenberg, CFPS
> > > > Fire Product Manager
> > > > Potter Electric Signal Company
> > > > www.pottersignal.com
> > > > 800-325-3936
> > > >
> > > > >>> "Dave Phelan" 10/23/2007 4:52 PM >>>
> > > > Something new to me popped up today as we are now using the 2002
> > editions of
> > > > 13 & 72 here.
> > > >
> > > > On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72
> > states that
> > > > the air supervisory sensor shall signal on loss of 10 PSI but also
> > on 10 PSI
> > > > greater than the system set pressure. Check out 5.13 for yourself
> > but I'm
> > > > thinking Ive never seen or tested for air greater than 10 PSI of the
> > set
> > > > pressure before.
> > > >
> > > > How is this being handled in the field during installs and
> > maintenance ?
> > > > Does the typical air pressure switch in the little red cover
> > actually cover
> > > > both loss and increase pressures?
> > > >
> > > > Thanks.
> > > >
> > > > Dave - a NJ AHJ
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > >
> > > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > > (Put the word unsubscribe in the subject field)
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > >
> > > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > > (Put the word unsubscribe in the subject field)
> > > >
> > >
> > >
> > > --
> > > Ron Greenman
> > > at home....
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> >
> >
> > --
> > Ron Greenman
> > at home....
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> 
> 
> -- 
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to