As I understand it the 7 psi is a minimum pressure that I think has it's origin from a minimum pressure required to blow off the cap and operate the sprinkler should there be minor adhesion. Pre-action by its nature requires supervision of the integrity of the piping and a drop in that pressure is necessary to operate the pre-action valve.
Mike Cabral ---- "David Powell (LES)" <[EMAIL PROTECTED]> wrote: > When I read NFPA 13 (2007 Edition), 7.3.2.4 Supervision my understanding > is that all pre-action systems require supervision of low air pressure > at 7 psi when there are 20 or more sprinklers in the system. Am I > missing something here? > > 7.3.2.4* Supervision. > 7.3.2.4.1 Sprinkler piping and fire detection devices shall be > automatically supervised where there are more than 20 sprinklers on the > system. > 7.3.2.4.2 Except as permitted by 7.3.2.4.3, air or nitrogen supervising > pressure for preaction systems shall be installed in conformance with > the dry pipe system air pressure and supply rules of 7.2.6. > 7.3.2.4.3 The relief valves required by 7.2.6 shall be permitted to be > omitted for the type of preaction system described in 7.3.2.1(1) when > the air pressure is supplied from a source that is not capable of > developing pressures in excess of 15 psi (1.0 bar). > 7.3.2.4.4 All preaction system types described in 7.3.2.1(2) and > 7.3.2.1(3) shall maintain a minimum supervising air or nitrogen pressure > of 7 psi (0.5 bar). > > David L. Powell > Fire Protection Officer > > LES > P.O. Box 1789 (all mail) > 1305 Avenue I > Eunice, NM 88231 > > Tel: +01 505 394 6021 > Mob: +01 505 602 0382 > Email: [EMAIL PROTECTED] > Web: www.nefnm.com > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Ron > Greenman > Sent: Tuesday, November 06, 2007 3:53 PM > To: [email protected] > Subject: Re: Supervisory Alarm - Low Air > > mike, > > I don't think you'll find any 13 requirement for low air alarms except > in refrigerated spaces. General low air monitoring is in 72 just like > high air. > > On 11/5/07, Mike Brown (TECH- GVL) <[EMAIL PROTECTED]> wrote: > > The monitoring of a high pressure is not in NFPA 13 or any other NFPA > > Pamphlet except in NFPA 72, and the NFPA 13 Committee has never seen > fit > > to put it in NFPA 13. I have never met anyone that could tell me why > it > > was in NFPA 72. > > Mike Brown > > > > -----Original Message----- > > From: [EMAIL PROTECTED] > > [mailto:[EMAIL PROTECTED] On Behalf Of Ron > > Greenman > > Sent: Wednesday, October 24, 2007 9:58 PM > > To: [email protected] > > Subject: Re: Supervisory Alarm - Low Air > > > > Of course! How foolish of me! Dave, can you send me your address. I > > lost it and I want to send your Tacoma Code Book. > > > > On 10/24/07, David de Vries <[EMAIL PROTECTED]> wrote: > > > How would you know? Simple, Ron. You would just check the log > where > > the building engineer dutifully recorded the air pressure on the > system > > on a weekly basis, as required by NFPA 25 where there is no electrical > > supervison, of course! > > > > > > lol > > > > > > Dave at Firetech Engineering Incorp. > > > > > > Ron Greenman <[EMAIL PROTECTED]> wrote: > > > I've always considered the high air supervision more critical than > > low > > > since a malfunctioning compressor that runs the air up will cause a > > > longer trip time whereas low air will just let you know that an > > > unwanted trip could happen if not attended to. Of course the > emphasis > > > is put on the low air because that trip rolls fire trucks, requires > a > > > technician to be summoned, disrupts the normal course of a day and > > > costs the owner money. All recordable events and therefore > > > statistically useful for proving one point or another. If, on the > > > other hand, you receive a high air you just fix the problem as a > piece > > > of equipment that needs maintenance. If a life or building was ever > > > lost because of high air delaying a trip how would anyone ever know? > > > The evidence would demonstrate an overwhelmed system but although it > > > might suggest it there is nothing I can think of that would > > > definitively demonstrate it was due to a delayed trip time. If a > bear > > > ....s in the woods...? > > > > > > On 10/24/07, Tim Frankenberg wrote: > > > > Dave, > > > > > > > > The requirement to monitor low and high air pressure has been in > the > > code before the 1993 edition of the National Fire Alarm Code. > > > > > > > > Most of the supervisory pressure switches installed are very much > > capable of monitoring both low and high air and have been able to for > > many, many years. More times than not, the high air condition is not > > being enforced by the AHJ. > > > > > > > > Kind Regards, > > > > > > > > Tim Frankenberg, CFPS > > > > > > > > Tim Frankenberg, CFPS > > > > Fire Product Manager > > > > Potter Electric Signal Company > > > > www.pottersignal.com > > > > 800-325-3936 > > > > > > > > >>> "Dave Phelan" 10/23/2007 4:52 PM >>> > > > > Something new to me popped up today as we are now using the 2002 > > editions of > > > > 13 & 72 here. > > > > > > > > On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72 > > states that > > > > the air supervisory sensor shall signal on loss of 10 PSI but also > > on 10 PSI > > > > greater than the system set pressure. Check out 5.13 for yourself > > but I'm > > > > thinking Ive never seen or tested for air greater than 10 PSI of > the > > set > > > > pressure before. > > > > > > > > How is this being handled in the field during installs and > > maintenance ? > > > > Does the typical air pressure switch in the little red cover > > actually cover > > > > both loss and increase pressures? > > > > > > > > Thanks. > > > > > > > > Dave - a NJ AHJ > > > > > > > > _______________________________________________ > > > > Sprinklerforum mailing list > > > > [email protected] > > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > > > To Unsubscribe, send an email > > to:[EMAIL PROTECTED] > > > > (Put the word unsubscribe in the subject field) > > > > > > > > _______________________________________________ > > > > Sprinklerforum mailing list > > > > [email protected] > > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > > > To Unsubscribe, send an email > > to:[EMAIL PROTECTED] > > > > (Put the word unsubscribe in the subject field) > > > > > > > > > > > > > -- > > > Ron Greenman > > > at home.... > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > To Unsubscribe, send an email > > to:[EMAIL PROTECTED] > > > (Put the word unsubscribe in the subject field) > > > > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > To Unsubscribe, send an email > > to:[EMAIL PROTECTED] > > > (Put the word unsubscribe in the subject field) > > > > > > > > > -- > > Ron Greenman > > at home.... > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email > > to:[EMAIL PROTECTED] > > (Put the word unsubscribe in the subject field) > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > > (Put the word unsubscribe in the subject field) > > > > > -- > Ron Greenman > at home.... > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > > DISCLAIMER: > This email transmission is confidential Louisiana Energy Services, L.P and > intended solely for the person or organization to which it is addressed. If > you are not the intended recipient, you must not copy, distribute or > disseminate the information or take any action in reliance of it. Any views > expressed in this message are those of the individual sender, except where > the sender specifically states them to be the views of any organization or > employer. If you have received this message in error, do not open any > attachment but please notify the sender (above) and delete this message from > your system. Please rely on your own virus check, as no responsibility is > taken by the sender for any damage arising out of any bug or virus. > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)