As I understand it the 7 psi is a minimum pressure that I think has it's origin 
from a minimum pressure required to blow off the cap and operate the sprinkler 
should there be minor adhesion. Pre-action by its nature requires supervision 
of the integrity of the piping and a drop in that pressure is necessary to 
operate the pre-action valve.

Mike Cabral

---- "David Powell (LES)" <[EMAIL PROTECTED]> wrote: 
> When I read NFPA 13 (2007 Edition), 7.3.2.4 Supervision my understanding
> is that all pre-action systems require supervision of low air pressure
> at 7 psi when there are 20 or more sprinklers in the system.  Am I
> missing something here?
> 
> 7.3.2.4* Supervision.
> 7.3.2.4.1  Sprinkler piping and fire detection devices shall be
> automatically supervised where there are more than 20 sprinklers on the
> system.
> 7.3.2.4.2  Except as permitted by 7.3.2.4.3, air or nitrogen supervising
> pressure for preaction systems shall be installed in conformance with
> the dry pipe system air pressure and supply rules of 7.2.6.
> 7.3.2.4.3  The relief valves required by 7.2.6 shall be permitted to be
> omitted for the type of preaction system described in 7.3.2.1(1) when
> the air pressure is supplied from a source that is not capable of
> developing pressures in excess of 15 psi (1.0 bar).
> 7.3.2.4.4  All preaction system types described in 7.3.2.1(2) and
> 7.3.2.1(3) shall maintain a minimum supervising air or nitrogen pressure
> of 7 psi (0.5 bar).
> 
> David L. Powell
> Fire Protection Officer
>  
> LES
> P.O. Box 1789 (all mail)
> 1305 Avenue I 
> Eunice, NM 88231
>  
> Tel:          +01 505 394 6021
> Mob:        +01 505 602 0382
> Email:      [EMAIL PROTECTED]
> Web:        www.nefnm.com
>  
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ron
> Greenman
> Sent: Tuesday, November 06, 2007 3:53 PM
> To: [email protected]
> Subject: Re: Supervisory Alarm - Low Air
> 
> mike,
> 
> I don't think you'll find any 13 requirement for low air alarms except
> in refrigerated spaces. General low air monitoring is in 72 just like
> high air.
> 
> On 11/5/07, Mike Brown (TECH- GVL) <[EMAIL PROTECTED]> wrote:
> > The monitoring of a high pressure is not in NFPA 13 or any other NFPA
> > Pamphlet except in NFPA 72, and the NFPA 13 Committee has never seen
> fit
> > to put it in NFPA 13.  I have never met anyone that could tell me why
> it
> > was in NFPA 72.
> > Mike Brown
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Ron
> > Greenman
> > Sent: Wednesday, October 24, 2007 9:58 PM
> > To: [email protected]
> > Subject: Re: Supervisory Alarm - Low Air
> >
> > Of course! How foolish of me! Dave, can you send me your address. I
> > lost it and I want to send your Tacoma Code Book.
> >
> > On 10/24/07, David de Vries <[EMAIL PROTECTED]> wrote:
> > > How would you know?  Simple, Ron.  You would just check the log
> where
> > the building engineer dutifully recorded the air pressure on the
> system
> > on a weekly basis, as required by NFPA 25 where there is no electrical
> > supervison, of course!
> > >
> > >   lol
> > >
> > >   Dave at Firetech Engineering Incorp.
> > >
> > > Ron Greenman <[EMAIL PROTECTED]> wrote:
> > >   I've always considered the high air supervision more critical than
> > low
> > > since a malfunctioning compressor that runs the air up will cause a
> > > longer trip time whereas low air will just let you know that an
> > > unwanted trip could happen if not attended to. Of course the
> emphasis
> > > is put on the low air because that trip rolls fire trucks, requires
> a
> > > technician to be summoned, disrupts the normal course of a day and
> > > costs the owner money. All recordable events and therefore
> > > statistically useful for proving one point or another. If, on the
> > > other hand, you receive a high air you just fix the problem as a
> piece
> > > of equipment that needs maintenance. If a life or building was ever
> > > lost because of high air delaying a trip how would anyone ever know?
> > > The evidence would demonstrate an overwhelmed system but although it
> > > might suggest it there is nothing I can think of that would
> > > definitively demonstrate it was due to a delayed trip time. If a
> bear
> > > ....s in the woods...?
> > >
> > > On 10/24/07, Tim Frankenberg wrote:
> > > > Dave,
> > > >
> > > > The requirement to monitor low and high air pressure has been in
> the
> > code before the 1993 edition of the National Fire Alarm Code.
> > > >
> > > > Most of the supervisory pressure switches installed are very much
> > capable of monitoring both low and high air and have been able to for
> > many, many years. More times than not, the high air condition is not
> > being enforced by the AHJ.
> > > >
> > > > Kind Regards,
> > > >
> > > > Tim Frankenberg, CFPS
> > > >
> > > > Tim Frankenberg, CFPS
> > > > Fire Product Manager
> > > > Potter Electric Signal Company
> > > > www.pottersignal.com
> > > > 800-325-3936
> > > >
> > > > >>> "Dave Phelan" 10/23/2007 4:52 PM >>>
> > > > Something new to me popped up today as we are now using the 2002
> > editions of
> > > > 13 & 72 here.
> > > >
> > > > On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72
> > states that
> > > > the air supervisory sensor shall signal on loss of 10 PSI but also
> > on 10 PSI
> > > > greater than the system set pressure. Check out 5.13 for yourself
> > but I'm
> > > > thinking Ive never seen or tested for air greater than 10 PSI of
> the
> > set
> > > > pressure before.
> > > >
> > > > How is this being handled in the field during installs and
> > maintenance ?
> > > > Does the typical air pressure switch in the little red cover
> > actually cover
> > > > both loss and increase pressures?
> > > >
> > > > Thanks.
> > > >
> > > > Dave - a NJ AHJ
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > >
> > > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > > (Put the word unsubscribe in the subject field)
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > >
> > > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > > (Put the word unsubscribe in the subject field)
> > > >
> > >
> > >
> > > --
> > > Ron Greenman
> > > at home....
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> >
> >
> > --
> > Ron Greenman
> > at home....
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> 
> 
> -- 
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> 
> 
> DISCLAIMER:
> This email transmission is confidential Louisiana Energy Services, L.P and 
> intended solely for the person or organization to which it is addressed. If 
> you are not the intended recipient, you must not copy, distribute or 
> disseminate the information or take any action in reliance of it. Any views 
> expressed in this message are those of the individual sender, except where 
> the sender specifically states them to be the views of any organization or 
> employer. If you have received this message in error, do not open any 
> attachment but please notify the sender (above) and delete this message from 
> your system. Please rely on your own virus check, as no responsibility is 
> taken by the sender for any damage arising out of any bug or virus.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________