Here's the reference; 2002 NFPA-72 5.13.2.2(2) "A pressure supervisory signal initiating device for a dry pipe sprinkler system shall indicated both high and low pressure conditions. The off normal signal shall be initiated when the pressure increases or decreases by 70kPa (10psi)."
2002 NFPA-72 is the 2006 IBC Chapter 35 Reference Standard. John Drucker Fire Protection Subcode Official New Jersey _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)