Here's the reference;

2002 NFPA-72 5.13.2.2(2) "A pressure supervisory signal initiating device
for a dry pipe sprinkler system shall indicated both high and low pressure
conditions. The off normal signal shall be initiated when the pressure
increases or decreases by 70kPa (10psi)."

2002 NFPA-72 is the 2006 IBC Chapter 35 Reference Standard.

John Drucker
Fire Protection Subcode Official
New Jersey