If the project specifications reference NFPA72 (as most of them do on the projects I encounter), well it seems you are sort'a put in a bind as to satisfying the engineer of record.
Just an observation, Ron -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman Sent: Tuesday, November 06, 2007 5:53 PM To: [email protected] Subject: Re: Supervisory Alarm - Low Air mike, I don't think you'll find any 13 requirement for low air alarms except in refrigerated spaces. General low air monitoring is in 72 just like high air. On 11/5/07, Mike Brown (TECH- GVL) <[EMAIL PROTECTED]> wrote: > The monitoring of a high pressure is not in NFPA 13 or any other NFPA > Pamphlet except in NFPA 72, and the NFPA 13 Committee has never seen fit > to put it in NFPA 13. I have never met anyone that could tell me why it > was in NFPA 72. > Mike Brown > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Ron > Greenman > Sent: Wednesday, October 24, 2007 9:58 PM > To: [email protected] > Subject: Re: Supervisory Alarm - Low Air > > Of course! How foolish of me! Dave, can you send me your address. I > lost it and I want to send your Tacoma Code Book. > > On 10/24/07, David de Vries <[EMAIL PROTECTED]> wrote: > > How would you know? Simple, Ron. You would just check the log where > the building engineer dutifully recorded the air pressure on the system > on a weekly basis, as required by NFPA 25 where there is no electrical > supervison, of course! > > > > lol > > > > Dave at Firetech Engineering Incorp. > > > > Ron Greenman <[EMAIL PROTECTED]> wrote: > > I've always considered the high air supervision more critical than > low > > since a malfunctioning compressor that runs the air up will cause a > > longer trip time whereas low air will just let you know that an > > unwanted trip could happen if not attended to. Of course the emphasis > > is put on the low air because that trip rolls fire trucks, requires a > > technician to be summoned, disrupts the normal course of a day and > > costs the owner money. All recordable events and therefore > > statistically useful for proving one point or another. If, on the > > other hand, you receive a high air you just fix the problem as a piece > > of equipment that needs maintenance. If a life or building was ever > > lost because of high air delaying a trip how would anyone ever know? > > The evidence would demonstrate an overwhelmed system but although it > > might suggest it there is nothing I can think of that would > > definitively demonstrate it was due to a delayed trip time. If a bear > > ....s in the woods...? > > > > On 10/24/07, Tim Frankenberg wrote: > > > Dave, > > > > > > The requirement to monitor low and high air pressure has been in the > code before the 1993 edition of the National Fire Alarm Code. > > > > > > Most of the supervisory pressure switches installed are very much > capable of monitoring both low and high air and have been able to for > many, many years. More times than not, the high air condition is not > being enforced by the AHJ. > > > > > > Kind Regards, > > > > > > Tim Frankenberg, CFPS > > > > > > Tim Frankenberg, CFPS > > > Fire Product Manager > > > Potter Electric Signal Company > > > www.pottersignal.com > > > 800-325-3936 > > > > > > >>> "Dave Phelan" 10/23/2007 4:52 PM >>> > > > Something new to me popped up today as we are now using the 2002 > editions of > > > 13 & 72 here. > > > > > > On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72 > states that > > > the air supervisory sensor shall signal on loss of 10 PSI but also > on 10 PSI > > > greater than the system set pressure. Check out 5.13 for yourself > but I'm > > > thinking Ive never seen or tested for air greater than 10 PSI of the > set > > > pressure before. > > > > > > How is this being handled in the field during installs and > maintenance ? > > > Does the typical air pressure switch in the little red cover > actually cover > > > both loss and increase pressures? > > > > > > Thanks. > > > > > > Dave - a NJ AHJ > > > > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > > > (Put the word unsubscribe in the subject field) > > > > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > > > (Put the word unsubscribe in the subject field) > > > > > > > > > -- > > Ron Greenman > > at home.... > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > > (Put the word unsubscribe in the subject field) > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > > (Put the word unsubscribe in the subject field) > > > > > -- > Ron Greenman > at home.... > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) Internal Virus Database is out-of-date. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM Internal Virus Database is out-of-date. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007 1:39 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)