What Tom said 100%. The only thing I might change is to put the two
test valves out on the roof. Pretty standard out here. Who wants to
drag hoses through stairwells?

On 11/22/07, Tom Duross <[EMAIL PROTECTED]> wrote:
> You don't have to flow 500 from just one valve, it can be 2.
> You can flow 250 on the 15th and 250 on the 16th or put 2 FDV's on the 16th.
> Why not pressure regulating valves (spkr/hose) and do it right?
> Restricting and reducing valves are junk and should be prohibited.
> Don't forget drain risers.
> Tom
>
>
>
> I guess I found the answer to one question. Pressure restricting hose valves
> I found were listed only upto 175 psi inlet pressure. Are there any for over
> 175 psi? My problem is with the pressure reducing valve (set at 165 psi) on
> the second riser, I can't get 100 psi at the upper floors (below the 13th).
> Any other options?
>
> Tony
>
>
> I'm working on a 16 storey residential building. The contractor wants to use
> 4" standpipe, resulting I need a 500 gpm @ 125 psi fire pump with the 76 psi
> static city water supply to provide 100 gpm at the top floor. (500 gpm @ 100
> psi at the most remote hose connection and automatic standpipe is the local
> requirement.) 13th floor up, the static pressure is less than 175 psi. I'm
> planning to have two risers. An express riser off the full pump pressure and
> a second riser after a pressure reducing valve set at 165 psi and located at
> the ground floor. Both 4 inch risers will be steel schedule 10 with
> victaulic fittings. All sprinkler heads will be standard (not rated for high
> pressure). The express riser will supply the sprinklers and 2 1/2" hose
> connections, 13th floor and up. I will be using pressure restricting hose
> valves set at 100 psi for each floor. Can I take the hose connections (using
> pressure restricting hose valves) from 12th floor down from the same express
> riser? (static pressure will range from 175 to 225 psi). Anything else wrong
> with this set up? Piping and fittings should be okay for less than 225 psi?
>
> Tony
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to