Other than creating some confusion on seismic requirements, what
difference does it make? what exactly is being challenged? I must
confess I haven't thought a lot about this.
Roland
On Nov 23, 2007, at 9:18 AM, [EMAIL PROTECTED] wrote:
Todd Williams wrote:
"Let's sit back and take a look at what we are trying to do here.
Install a sprinkler system to provide satisfactory protection against
fire in a particular building. Where or how the sprinklers are
connected to pipes should not be an issue, as long as adequate water
gets to the fire (with allowance for minimum pipe size, etc)."
Agree completely, so why the explicit language in 2007 defining a
branch
line? As you state, it seems any pipe or any arrangement of piping
on a
hydraulically calculated wet pipe system is OK.
Yes, this is an actual case - I couldn't have made this up by myself.
Bill Brooks
-------- Original Message --------
Subject: RE: Branch Lines / Cross Mains
From: Todd Williams - FPDC <[EMAIL PROTECTED]>
Date: Fri, November 23, 2007 10:54 am
To: [email protected]
Let's sit back and take a look at what we are trying to do here.
Install a sprinkler system to provide satisfactory protection against
fire in a particular building. Where or how the sprinklers are
connected to pipes should not be an issue, as long as adequate water
gets to the fire (with allowance for minimum pipe size, etc).
Semantics over what the definition of a branch line is? I'm waiting
for the AHJ to come at me with the comment that I can't attach a 1"
drop to a 6" main because it doesn't meet the definition of a branch
line. Bill, did someone actually challenge you on this? Tell him the
drop is a 1" branch line looking down and the feed to the pendent
sprinkler off the branch line is fed by an arm-over.
At 09:49 AM 11/23/2007, you wrote:
Agree with the "why shouldn't we?" but I'm looking for the "where
does
it say we can?". Although the simple answer is "we do it all the
time",
the 2007 text change language has created a situation where the only
place to attach a SINGLE sprinkler is a branch line. The 2002 text
could have been interpreted this way but the 2007 has made it
explicit.
I have a branch line with 5 outlets. The first two are upright
sprinklers, the third one feeds two pendents under a duct, the
last two
are uprights.
I think all of us would consider this a branch line, but the new
definition now states that part of this branch line is a cross main
since the piece under the duct is an independent branch line. Then,
since the definition of a cross main does not include a sprinkler,
the
last two heads have to be piped from a single outlet on the "cross
main".
Twisted logic I agree but I can't find another definition to get
me out
of this AHJ mess.
For a hydraulically calculated system, who cares where you add a
sprinkler? Can a single sprinkler or a branch line be fed from the
side
of a riser as long as you maintain waterflow alarm capability?
Bill Brooks
-------- Original Message --------
Subject: Re: Branch Lines / Cross Mains
From: "Ron Greenman" <[EMAIL PROTECTED]>
Date: Wed, November 21, 2007 7:24 pm
To: [email protected]
Just as a standpipe can serve double duty as a sprinkler riser why
shouldn't a cross-main or feed main also serve as a branch line.
Ultimately were always talking about one or more standardized
holes in
our hose leaking in a defined area. Who cares what size and name you
use for the hose as long as it will properly support the leaks.
Enough
wet guy stuff. Nearly time to eat.
On Nov 21, 2007 12:59 PM, John Drucker <[EMAIL PROTECTED]>
wrote:
For the feed main arrangement is there a method of waterflow
detection
and annunciation corresponding to the smallest sprinkler ?
Happy Thanksgiving all !
John
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
Roland
Huggins
Sent: Wednesday, November 21, 2007 3:51 PM
To: [email protected]
Subject: Re: Branch Lines / Cross Mains
certainly. The definitions do not address such hybrid items but that
doesn't stop one from doing it.
Roland
On Nov 21, 2007, at 12:11 PM, [EMAIL PROTECTED] wrote:
Can a sprinkler head be connected to a cross main or feed main
(directly or by way of a sprig, drop, arm over, or return bend)?
After you answer the question read the revised definition of a
branch
line in 2007, 3.5.1.
Bill Brooks
William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED] (Put the word unsubscribe in the subject
field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)