Agree with the "why shouldn't we?" but I'm looking for the "where does
it say we can?".  Although the simple answer is "we do it all the time",
the 2007 text change language has created a situation where the only
place to attach a SINGLE sprinkler is a branch line.  The 2002 text
could have been interpreted this way but the 2007 has made it explicit.

I have a branch line with 5 outlets.  The first two are upright
sprinklers, the third one feeds two pendents under a duct, the last two
are uprights.

I think all of us would consider this a branch line, but the new
definition now states that part of this branch line is a cross main
since the piece under the duct is an independent branch line.  Then,
since the definition of a cross main does not include a sprinkler, the
last two heads have to be piped from a single outlet on the "cross
main".

Twisted logic I agree but I can't find another definition to get me out
of this AHJ mess.

For a hydraulically calculated system, who cares where you add a
sprinkler?  Can a single sprinkler or a branch line be fed from the side
of a riser as long as you maintain waterflow alarm capability?

Bill Brooks

-------- Original Message --------
Subject: Re: Branch Lines / Cross Mains
From: "Ron Greenman" <[EMAIL PROTECTED]>
Date: Wed, November 21, 2007 7:24 pm
To: [email protected]

Just as a standpipe can serve double duty as a sprinkler riser why
shouldn't a cross-main or feed main also serve as a branch line.
Ultimately were always talking about one or more standardized holes in
our hose leaking in a defined area. Who cares what size and name you
use for the hose as long as it will properly support the leaks. Enough
wet guy stuff. Nearly time to eat.

On Nov 21, 2007 12:59 PM, John Drucker <[EMAIL PROTECTED]> wrote:
> For the feed main arrangement is there a method of waterflow detection
> and annunciation corresponding to the smallest sprinkler ?
>
> Happy Thanksgiving all !
>
> John
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Roland
> Huggins
> Sent: Wednesday, November 21, 2007 3:51 PM
> To: [email protected]
>
> Subject: Re: Branch Lines / Cross Mains
>
> certainly. The definitions do not address such hybrid items but that
> doesn't stop one from doing it.
>
> Roland
>
> On Nov 21, 2007, at 12:11 PM, [EMAIL PROTECTED] wrote:
>
> > Can a sprinkler head be connected to a cross main or feed main
> > (directly or by way of a sprig, drop, arm over, or return bend)?
> >
> > After you answer the question read the revised definition of a branch
> > line in 2007, 3.5.1.
> >
> > Bill Brooks
> >
> > William N. Brooks, P.E.
> > Brooks Fire Protection Engineering Inc.
> > 372 Wilett Drive
> > Severna Park, MD 21146
> > 410-544-3620 Phone
> > 410-544-3032 FAX
> > 412-400-6528 Cell
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> > [EMAIL PROTECTED] (Put the word unsubscribe in the subject
> > field)
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to