Roland, See NFPA-13, par 8.16.4.1.5, for heat tracing of branch lines. Can we heat trace 1-inch steel piping which supplies one dry pendent sprinkler which protects a loading dock area? The 1-inch piping is on the end of a "branch line" which penetrates the exterior wall, runs inside a boxed canopy over a loading area, and is used to supply one dry pendent sprinkler to protect the loading area. The exterior wall is constructed that using a dry sidewall sprinklers is not an option.
The older standards had a Formal Interpretation that did not allow heat tracing for branch lines, and I don't know if there is any heat tracing specifically listed for branch lines. rick matsuda, city of dallas -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Monday, November 26, 2007 9:51 AM To: [email protected] Subject: Re: Branch Lines / Cross Mains Other than creating some confusion on seismic requirements, what difference does it make? what exactly is being challenged? I must confess I haven't thought a lot about this. Roland On Nov 23, 2007, at 9:18 AM, [EMAIL PROTECTED] wrote: > Todd Williams wrote: > > "Let's sit back and take a look at what we are trying to do here. > Install a sprinkler system to provide satisfactory protection against > fire in a particular building. Where or how the sprinklers are > connected to pipes should not be an issue, as long as adequate water > gets to the fire (with allowance for minimum pipe size, etc)." > > Agree completely, so why the explicit language in 2007 defining a > branch > line? As you state, it seems any pipe or any arrangement of piping > on a > hydraulically calculated wet pipe system is OK. > > Yes, this is an actual case - I couldn't have made this up by myself. > > Bill Brooks _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)