Great example of this point. There's a schedule 40 riser with cut
grooves in one of the Pike Place Market Buildings. This is riser is a
twisty thing made of several small sections of 6" pipe. Several of
these sections developed leaks at the cut-grooves (this time
definitely at the seam weld). After the second time we figured all
these short sections were probably fabbed from the same joint and so
replaced everything. I don't know if the cuts were within spec or not
and because the work always had to be done between 2 AM & 6AM I really
didn't care. So, what is the equivalent schedule of the pipe in a
properly done cut groove?

On 1/27/08, Joe Hankins <[EMAIL PROTECTED]> wrote:
> The life of a sprinkler system is influenced by local conditions, but
> one thing that can be said across the board is that you can't base the
> life expectancy of a schedule 10 system on the longevity of an existing
> schedule 40 system.  Under equal conditions, schedule 10 pipe has
> roughly one half the life expectancy of schedule 40 pipe.