My two cents:

6" sch 40 wall thickness .289 (can be a little different from chart to chart.) 
Sdt cut groove depth .085 which leaves .204 wall about the same as 2.5" sch 40 
wall thickness. Sch 10 -  6" std wall is .109. Cut groove sch 40 is almost 
twice the wall thickness of 6" sch 10.

In my view cut grooving would be the preferred method of installing sch 40 
pipe. . . wall thickness equal time. The roll groove also generates a dam 
effect and contributes to pooling of condensate at the joint which provides 
ideal conditions for corrosion. Air + Water + Steel = Corrosion' MIC is a 
secondary source of corrosion in fire sprinkler systems there is always some 
form of corrosion first which sets up the condition for MIC to thrive.

Mike Cabral

---- Ron Greenman <[EMAIL PROTECTED]> wrote: 
> Joe,
> 
> Great example of this point. There's a schedule 40 riser with cut
> grooves in one of the Pike Place Market Buildings. This is riser is a
> twisty thing made of several small sections of 6" pipe. Several of
> these sections developed leaks at the cut-grooves (this time
> definitely at the seam weld). After the second time we figured all
> these short sections were probably fabbed from the same joint and so
> replaced everything. I don't know if the cuts were within spec or not
> and because the work always had to be done between 2 AM & 6AM I really
> didn't care. So, what is the equivalent schedule of the pipe in a
> properly done cut groove?
> 
> On 1/27/08, Joe Hankins <[EMAIL PROTECTED]> wrote:
> > The life of a sprinkler system is influenced by local conditions, but
> > one thing that can be said across the board is that you can't base the
> > life expectancy of a schedule 10 system on the longevity of an existing
> > schedule 40 system.  Under equal conditions, schedule 10 pipe has
> > roughly one half the life expectancy of schedule 40 pipe.
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> 
> 
> -- 
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to