Did there seem to be any pattern to the location of the pinholes (such as
along the bottom of the pipe, or at the roll grooves, or at the pipe weld
seams, etc)?

Ed Kramer
Littleton, CO


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Sunday, January 27, 2008 5:29 AM
To: [email protected]
Subject: RE: Fire sprinkler question

As for extremes of what did and didn't work, I'd offer the following off the
top of my head:

1911 & 1916 wet systems at SS White Building, 12 stories in downtown Phila
with steam pump boosting city water with city steam- did internal inspection
to investigate feasibility of re-using 3/4" lines in a condo conversion from
mfg; clean as a whistle. We did use new heads :)

2001 installation of Allied galv sch 10 at an office building west shore of
Harrisburg, wood truss attic dry systems; After 3 years in service, with
nothing done to the system but install, hydro, air test, acceptance test,
drain and place in initial service- no ITM whatsoever- pinhole leaks tripped
the system a few times and we ripped it all out and replaced it 3 years
after putting it in service. Analysis indicated it was NOT MIC and, after
the system was completely replaced at no cost to the owner (and no
reimbursement from mfr) the property owner asked us to not bid their
addition. Just makes you wonder what would it take to make them happy?
Shoulda told em "One Year Warranty, have a nice day" but we did what we
thought was the right thing to do. Just can't make some people happy, I
guess.

GLC