As I was searching in NFPA codes, I noticed that there are not that much 
information about hose reels. Can we use 1 in. semi rigid hose on hose reels 
instead of lay flat hoses in occupancies required 1 1/2 hose stations? Because 
using a hose reel is much more easier for occupants, Is there any guide when I 
can use hose reels instead of lay flat hoses?
   
  What about minimum pressure requirements? As per NFPA-14 residual pressure 
should be 65 psi at the outlet of the hydraulically most remote 1 1/2 in. hose 
station, but as per my experience hose reels need lower pressure to work fine 
in comparison with lay flat hoses. Do I need 65 psi pressure even if I use hose 
reels?
   
  The reason I am asking this question is that in a combined system, as my 
standpipe system needs much more pressure than my sprinkler system, if I can 
reduce my standpipe required pressure using hose reels I can save much in 
selection of smaller fire pump & water tank, but I am not sure if I am allowed.
  I was checking a hose reel manufacture data sheets and I noticed that a 1 in. 
hose reel in 45 psi pressure flow is 21 Gpm with throw distance of 40 ft. Isn't 
it enough for a occupant use? am I allowed to design based on 45 psi instead of 
65 psi in 1 1/2 in outlets while I am using hose reels?
  Thanks,
  Reza

       
---------------------------------