If you're talking about the engine generator, NFPA 110 (5.6.6) requires remote alarms outside the engine room at a "work site observable by personnel". A variety of engine conditions must be displayed and are listed in Table 5.6.5.2. The "Control Switch not in Automatic Position" is among the alarms that must be annunciated.
If you are talking about the diesel engine driver for the pump, the only alarm points that I am aware of are contained in NFPA 20, which include "Controller - Manual Off". These are required to be displayed as a supervisory alarm on the fire alarm system. Ray Schmid, P.E. Schmid and Associates Fire Protection Engineers -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of danarbel Sent: Tuesday, February 19, 2008 6:33 AM To: [email protected] Subject: RE: Diesel vs Electric I'm still asking for a reference requiring supervision of the Generator Status as applied to Diesel or Electric pump in the NFPA 20. For instance, who has to know that the main switch of the generator is not in automatic mode? Dan Dan Arbel Tel: 972-4-8243337 Fax: 972-4-8243278 M: 972-52-2810593 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Monday, February 18, 2008 9:54 PM To: [email protected] Subject: RE: Diesel vs Electric That's as may be, but on high-rise buildings the code requires an emergency gen-set anyway, so once that's fait accompli the economics of the pump as a stand-alone line item generally favors the electric. Depending on size, it may favor electric a LOT - the wild card isn't the cost of the pump itself, but the size of the main panel and service on the electrical side. Once you get up and over 250 HP, it can be VERY expensive to feed the building (and can lead to a second transformer in SOME states and under the jurisdiction of SOME utilities) and a diesel starts to make sense again. Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Friday, February 15, 2008 9:37 AM To: [email protected] Subject: RE: Diesel vs Electric We have found that a diesel pump alone is more cost effective than an electric with a gen set. Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Charles Thurston Sent: Friday, February 15, 2008 7:32 AM To: [email protected] Subject: Diesel vs Electric Hello sprinklerforum, I am looking for opinions on installing a Diesel fire pump Vs installing an Electric fire pump and Gen Set. I have a location that is being cut loose from the "Site Wide" fire pump loop now owned by others. -- Best regards, Charles mailto:[EMAIL PROTECTED] Coastal Fire Protection _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.516 / Virus Database: 269.20.7/1285 - Release Date: 18/02/2008 05:50 No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.516 / Virus Database: 269.20.7/1285 - Release Date: 18/02/2008 05:50 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)