If he doesn't want to make any concessions or adjustments for fire
protection, then design to the worst case and tell him that is the
deal. If he balks at it, then tell him he will have to change his
set-up. If he is welding next the plastics and flammable oils, the
protect for it. The AHJ might have a little input on this as well.
At 10:20 AM 2/24/2008, you wrote:
I have an interesting design/build project that just showed up.
Metal building, purlins, solid tapered beams (1:12) on columns, space
manufactured, 75' w x 100' l x 30' h.
Radiant heated, insulated, open with a short 25' end mezzanine for Offices,
etc.
It's a plumber's building, and to be used for services as he needs them.
I asked:
Storage? Yes, when needed.
Racks? Yes, when needed but movable on casters so we can move them outside
if they're in the way.
Welding? Yes, when needed.
Plastics? Yes, when needed.
This guy does a lot of prefab plumbing, soil pipe to pex, and is using this
place as a staging/fabrication facility.
I've tried two approaches with him. One, let's just design for the worst
and two, let's try and limit your operations.
He obviously doesn't want to classify the use as a welding shop with 25'
racks of pvc fittings loose in bins jammed against each other 10' from the
welder's curtain and has said why not just tell me what the simplest bare
open system will cost and we'll try and keep things as safe as we can. Hmmm.
I've suggested we include his insurer and he balked but after I told him
without some agreement, his policy could change yearly upon inspection. I
think he understands. I think the biggest issue is trying to predict what
work may come his way and then dictate what the building will be used for.
He's old union and very large. He could be doing anything from housing to
petrochemical work and anything in between.
Any thoughts? I was thinking of copying the section on Storage and letting
him read it but I think he'd get 2 pages in and drop it.
I realize it's like asking how long is a piece of string, but how have you
approached this?
Tom
GRS
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)