Forum,

Is a Pressure Reducing valve, such as the Tyco PRV-1, allowed to be 
installed on the main sprinkler/standpipe header downstream of an electric 
fire pump.  I know pressure relief valve is only permitted on diesel fire 
pumps.  I have an estimated flow of 1,000GPM @ 165 psi.  I want to limit 
the majority of system to 175 psi and I don't want to overload the system 
during churn conditions.  NFPA 13 and 14 seem to allow this but NFPA 20 
says, "No pressure-regulating devices shall be installed in the discharge 
pipe except as permitted in this standard."

John Kaminski
Burt Hill
724-431-1388
http://www.burthill.com