Watch where you connect the jockey pump discharge. For the fire pump controller to function correctly the JP discharge should be between the control valve on the discharge side of the fire pump and the PRV. Bobby McCullough
________________________________ From: [EMAIL PROTECTED] on behalf of Roland Huggins Sent: Fri 3/28/2008 2:37 PM To: [email protected] Subject: Re: Pressure Reducing Valve The jurisdiction for NFPA 20 ends at the last control valve they call for at the discharge side and NFPA 13 / 14 etc rule from that point on. So no PRV before that valve but afterwards is AOK. Roland On Mar 28, 2008, at 11:16 AM, [EMAIL PROTECTED] wrote: > Forum, > > Is a Pressure Reducing valve, such as the Tyco PRV-1, allowed to be > installed on the main sprinkler/standpipe header downstream of an > electric > fire pump. I know pressure relief valve is only permitted on > diesel fire > pumps. I have an estimated flow of 1,000GPM @ 165 psi. I want to > limit > the majority of system to 175 psi and I don't want to overload the > system > during churn conditions. NFPA 13 and 14 seem to allow this but > NFPA 20 > says, "No pressure-regulating devices shall be installed in the > discharge > pipe except as permitted in this standard." > > John Kaminski > Burt Hill > 724-431-1388 > http://www.burthill.com > > > This email is intended for named recipients only. > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)