Sorry, Jay, didn't note it was a diesel- Don't cut any wires- pull em, plug off half the ignitors.
Seriously, I wouldn't put the PRV ahead of the pump, what if it failed to open when needed? glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jay Stough Sent: Tuesday, April 22, 2008 2:42 PM To: AFSA Sprinkler Forum Subject: Pressure reducing valve We have a customer that has a 1500gpm @ 150 psi pump in their facility. When the pump was originally installed years ago, the incoming street pressure was between 40 & 45 psi. So when the pump ran weekly, the pressure relief valve on the pump was set at 190 psi and everything was OK. All the fittings in the basement and first floor are 300 psi fittings. Now the water company has increased the pressure in the area to 110 psi static ( how many areas have this problem 15 years later?), so when the pumps runs each week, you are dumping thousands of gallons of water, especially since it's a diesel and runs for a 1/2 hour. The customer does not want to get rid of the pump because they are planning large additions in the next few years and are not sure if they will need it or not. Is it OK to put a pressure reducing valve after the backflow and about 35' from the pump suction? 20 says no valve except an OS & Y shall be installed in the suction piping. Any ideas? Joseph C. Stough SET, CFPS Tilley Fire Equipment Co. Tel. 215-345-8066 X22 Fax: 215-345-9357 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)