Any reason you can't pipe relief va discharge to pump suction? Or put the prv between the discharge and main relief?
Cut a few of the leads to the motor? glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Tuesday, April 22, 2008 2:58 PM To: [email protected] Subject: RE: Pressure reducing valve I'm contemplating the exact same thing myself right now. Too bad we can't get a suction control valve to work in reverse. Tom We have a customer that has a 1500gpm @ 150 psi pump in their facility. When the pump was originally installed years ago, the incoming street pressure was between 40 & 45 psi. So when the pump ran weekly, the pressure relief valve on the pump was set at 190 psi and everything was OK. All the fittings in the basement and first floor are 300 psi fittings. Now the water company has increased the pressure in the area to 110 psi static ( how many areas have this problem 15 years later?), so when the pumps runs each week, you are dumping thousands of gallons of water, especially since it's a diesel and runs for a 1/2 hour. The customer does not want to get rid of the pump because they are planning large additions in the next few years and are not sure if they will need it or not. Is it OK to put a pressure reducing valve after the backflow and about 35' from the pump suction? 20 says no valve except an OS & Y shall be installed in the suction piping. Any ideas? Joseph C. Stough SET, CFPS _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)