Are you saying that you want both a pressure reducing valve and a
pressure relief valve?   (Roland, you of all people should know not to
just use the term PRV!)  The Tyco PRV-1 is a pressure reducing valve,
but you reference putting a relief valve on the system.   If you want a
steady-state downstream pressure, you need a pressure control valve.
Reducing valves can manage downstream pressure, but work on a
differential basis and thus the downstream pressure is a curve, not a
steady state.  As best as I can tell, you don't want a relief valve at
all.

As Ro said, don't worry about the downstream thing.   NFPA 20 is
creating a new chapter - 4 or 5, TBD - for high-rise pump requirements
and that discrepancy should go away at the end of their current cycle.
But remember that 14 requires that you provide redundant valves if you
propose to put a PRV-1 downstream of the pump in a high-rise combo
system where failure of the reducing valve could impact more than two
Class I hose connections.   

Steve Leyton
Protection Design & Consulting



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, March 28, 2008 11:17 AM
To: [email protected]
Subject: Pressure Reducing Valve

Forum,

Is a Pressure Reducing valve, such as the Tyco PRV-1, allowed to be 
installed on the main sprinkler/standpipe header downstream of an
electric 
fire pump.  I know pressure relief valve is only permitted on diesel
fire 
pumps.  I have an estimated flow of 1,000GPM @ 165 psi.  I want to limit

the majority of system to 175 psi and I don't want to overload the
system 
during churn conditions.  NFPA 13 and 14 seem to allow this but NFPA 20 
says, "No pressure-regulating devices shall be installed in the
discharge 
pipe except as permitted in this standard."

John Kaminski
Burt Hill
724-431-1388
http://www.burthill.com


This email is intended for named recipients only.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to