Are you saying that you want both a pressure reducing valve and a pressure relief valve? (Roland, you of all people should know not to just use the term PRV!) The Tyco PRV-1 is a pressure reducing valve, but you reference putting a relief valve on the system. If you want a steady-state downstream pressure, you need a pressure control valve. Reducing valves can manage downstream pressure, but work on a differential basis and thus the downstream pressure is a curve, not a steady state. As best as I can tell, you don't want a relief valve at all.
As Ro said, don't worry about the downstream thing. NFPA 20 is creating a new chapter - 4 or 5, TBD - for high-rise pump requirements and that discrepancy should go away at the end of their current cycle. But remember that 14 requires that you provide redundant valves if you propose to put a PRV-1 downstream of the pump in a high-rise combo system where failure of the reducing valve could impact more than two Class I hose connections. Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Friday, March 28, 2008 11:17 AM To: [email protected] Subject: Pressure Reducing Valve Forum, Is a Pressure Reducing valve, such as the Tyco PRV-1, allowed to be installed on the main sprinkler/standpipe header downstream of an electric fire pump. I know pressure relief valve is only permitted on diesel fire pumps. I have an estimated flow of 1,000GPM @ 165 psi. I want to limit the majority of system to 175 psi and I don't want to overload the system during churn conditions. NFPA 13 and 14 seem to allow this but NFPA 20 says, "No pressure-regulating devices shall be installed in the discharge pipe except as permitted in this standard." John Kaminski Burt Hill 724-431-1388 http://www.burthill.com This email is intended for named recipients only. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)