We have a customer that has a 1500gpm @ 150 psi pump in their facility.
When the pump was originally installed years ago, the incoming street
pressure was between 40 & 45 psi. So when the pump ran weekly, the pressure
relief valve on the pump was set at 190 psi and everything was OK. All the
fittings in the basement and first floor are 300 psi fittings. Now the
water company has increased the pressure in the area to 110 psi static ( how
many areas have this problem 15 years later?), so when the pumps runs each
week, you are dumping thousands of gallons of water, especially since it's a
diesel and runs for a 1/2 hour. The customer does not want to get rid of
the pump because they are planning large additions in the next few years and
are not sure if they will need it or not. Is it OK to put a pressure
reducing valve after the backflow and about 35' from the pump suction? 20
says no valve except an OS & Y shall be installed in the suction piping.
Any ideas?