You can't do the top 4 floors of a residential high-rise as #13R?
No elderly apartments over tire storage?

Seriously, most stretch I've seen is for PA recognizing a basement that was
partially above grade and 4 stories above qualifying for 13R before we
adopted the I-codes and were on early 80's BOCA.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Friday, April 18, 2008 8:55 AM
To: [email protected]
Subject: RE: 13R Classification

Plus, it's mixed use. 13 throughout.
One building, one use, one standard, one design.

Tom
GRS

Hello Bobby,

I was taught if there is a 5th floor it is not 13R. The whole building has
to be 13.

Friday, April 18, 2008, 8:16:04 AM, you wrote:

> A question has been asked in our office and I would appreciate the
opinions
> of the forum as to the intent of 13R.

>  There is a 5 story building, bottom floor is mercantile and the top 4
> floors are residential. "NFPA13R Standard for the Installation of
Sprinkler
> Systems in Residential Occupancies up to and Including Four Stories in
> Height." The debate is; is the intent of the standard to be that anything
> over 4 stories cannot be classified as 13R or can the building in question
> be classified as 13R because there are 4 stories in height for residential
> occupancy?

>

> Thank you in advance.

>

> Bobby Gillett

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to