I would define "staying within one standard" to mean using NFPA 13R as the basis but using NFPA 13 for areas outside the dwelling unit. Same would be true for an NFPA 13 design where this document might refer you to another standard.
Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell -------- Original Message -------- Subject: RE: 13R Classification From: "Bobby Gillett" <[EMAIL PROTECTED]> Date: Fri, April 18, 2008 2:36 pm To: <[email protected]> Thank you for your responses I believe you settled our debate although now they are asking me "... where are they getting you have to stay within one standard?" (13 or 13R). Thanks again. Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Friday, April 18, 2008 10:17 AM To: [email protected] Subject: RE: 13R Classification There is a proposal in the current ROP (13R-58, Log #37 - Committee Action: Accept) that will hopefully give better direction with regard to this (these) issue(s). Capsule version of the material is to clarify that if a building (such as a pedestal or podium type) is divided into separate buildings as defined by the code, that 13R is applicable in the R-group building and 13 would apply to the other. This represents a change from what we've been saying (myself, AFSA, here in this thread) WRT to "mixed use" buildings requiring a 13 design unconditionally. But the proposed language makes very clear that these provisions apply to buildings that are no more than 4 stories above "grade plane" (also as defined by the code), so if we're talking about a 5-story structure (per code), the applicable standard is 13. Period. Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez Sent: Friday, April 18, 2008 6:53 AM To: [email protected] Subject: RE: 13R Classification Could you consider this 2 separate areas if the building falls under the "pedestal" design of section 508 (2003 IBC)? I have an excerpt from the 2006 Building Safety Journal that may help. "In addition to the basic requirement that the pedestal building be of Type IA construction and separated from the buildings above by a horizontal ceiling/floor/roof assembly having a minimum 3-hour fire resistance rating, the following limitations also apply. * Per Section 508.2, Item 4, Exceptions, the use of the pedestal building is restricted to any combination of the following: * S-2 enclosed parking garage; * multiple Group A uses limited to those having assembly rooms with occupant loads of less than 300 each; * Group B uses; * Group M uses; and * entry lobbies, mechanical rooms, storage areas and similar uses incidental to the operation of the building. * Per Section 508.2, Item 3, the use of the buildings above the pedestal building is restricted to any combination of the following: * Group R uses, * multiple Group A uses limited to those having assembly rooms with occupant loads of less than 300 each, * Group B uses and * Group M uses. " Hope this helps. Bobby, leave me email if you want the full article. Thanks, Dewayne Martinez, CET Design Build Fire Protection [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Friday, April 18, 2008 7:55 AM To: [email protected] Subject: RE: 13R Classification Plus, it's mixed use. 13 throughout. One building, one use, one standard, one design. Tom GRS Hello Bobby, I was taught if there is a 5th floor it is not 13R. The whole building has to be 13. Friday, April 18, 2008, 8:16:04 AM, you wrote: > A question has been asked in our office and I would appreciate the opinions > of the forum as to the intent of 13R. > There is a 5 story building, bottom floor is mercantile and the top 4 > floors are residential. "NFPA13R Standard for the Installation of Sprinkler > Systems in Residential Occupancies up to and Including Four Stories in > Height." The debate is; is the intent of the standard to be that > anything over 4 stories cannot be classified as 13R or can the > building in question be classified as 13R because there are 4 stories > in height for residential occupancy? > > Thank you in advance. > > Bobby Gillett _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)