Could you consider this 2 separate areas if the building falls under the "pedestal" design of section 508 (2003 IBC)? I have an excerpt from the 2006 Building Safety Journal that may help.
"In addition to the basic requirement that the pedestal building be of Type IA construction and separated from the buildings above by a horizontal ceiling/floor/roof assembly having a minimum 3-hour fire resistance rating, the following limitations also apply. * Per Section 508.2, Item 4, Exceptions, the use of the pedestal building is restricted to any combination of the following: * S-2 enclosed parking garage; * multiple Group A uses limited to those having assembly rooms with occupant loads of less than 300 each; * Group B uses; * Group M uses; and * entry lobbies, mechanical rooms, storage areas and similar uses incidental to the operation of the building. * Per Section 508.2, Item 3, the use of the buildings above the pedestal building is restricted to any combination of the following: * Group R uses, * multiple Group A uses limited to those having assembly rooms with occupant loads of less than 300 each, * Group B uses and * Group M uses. " Hope this helps. Bobby, leave me email if you want the full article. Thanks, Dewayne Martinez, CET Design Build Fire Protection [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Friday, April 18, 2008 7:55 AM To: [email protected] Subject: RE: 13R Classification Plus, it's mixed use. 13 throughout. One building, one use, one standard, one design. Tom GRS Hello Bobby, I was taught if there is a 5th floor it is not 13R. The whole building has to be 13. Friday, April 18, 2008, 8:16:04 AM, you wrote: > A question has been asked in our office and I would appreciate the opinions > of the forum as to the intent of 13R. > There is a 5 story building, bottom floor is mercantile and the top 4 > floors are residential. "NFPA13R Standard for the Installation of Sprinkler > Systems in Residential Occupancies up to and Including Four Stories in > Height." The debate is; is the intent of the standard to be that > anything over 4 stories cannot be classified as 13R or can the > building in question be classified as 13R because there are 4 stories > in height for residential occupancy? > > Thank you in advance. > > Bobby Gillett _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)