Apart from considering the V over I concept ridiculous I think we've beaten this about multiple times. First is that you can't have a building over another building and secondly 13R say "NOT OVER FOUR STORIES." It doesn't say not over four stories except when ______ (fill in the blank). I do know of some jurisdictions around here that allow in their local ordinances for 13R for the residential portions in mixed use occupancies but only if the aggregate does not exceed four stories. On the other hand I know of two horrible "13R" apartments of eight stories on a hillside where the first three stories aren't "stories" because they're partially buried in the hillside (arguable although they are residential) and type I and the next five are stick-built but OK because the top floor is occupied "attic" space used for the second floor of the fourth floor "view" apartments (the view is of a shopping mall and Interstate 5) and sprinklered, and so it's only four stories with a "converted" (converted at the time of construction on the original approved plans) attic. The only way I can see this happening is a developer arguing with a politician and the Building Official being ordered to let this one through (this is the ecotopia of the West Coast where ,at least direct, baksheesh is not a way of life. When I asked the fire marshal how they got approved he just shrugged his shoulders and looked skyward.
On Fri, Apr 18, 2008 at 6:53 AM, Dewayne Martinez <[EMAIL PROTECTED]> wrote: > Could you consider this 2 separate areas if the building falls under the > "pedestal" design of section 508 (2003 IBC)? I have an excerpt from the > 2006 Building Safety Journal that may help. > > "In addition to the basic requirement that the pedestal > building be of Type IA construction and separated from the > buildings above by a horizontal ceiling/floor/roof assembly > having a minimum 3-hour fire resistance rating, the following > limitations also apply. > * Per Section 508.2, Item 4, Exceptions, the use of the > pedestal building is restricted to any combination of the > following: > * S-2 enclosed parking garage; > * multiple Group A uses limited to those having assembly > rooms with occupant loads of less than 300 each; > * Group B uses; > * Group M uses; and > * entry lobbies, mechanical rooms, storage areas and > similar uses incidental to the operation of the building. > * Per Section 508.2, Item 3, the use of the buildings above > the pedestal building is restricted to any combination of > the following: > * Group R uses, > * multiple Group A uses limited to those having assembly > rooms with occupant loads of less than 300 each, > * Group B uses and > * Group M uses. " > > Hope this helps. Bobby, leave me email if you want the full article. > Thanks, > Dewayne Martinez, CET > Design Build Fire Protection > [EMAIL PROTECTED] > > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Tom > Duross > Sent: Friday, April 18, 2008 7:55 AM > To: [email protected] > Subject: RE: 13R Classification > > > > Plus, it's mixed use. 13 throughout. > One building, one use, one standard, one design. > > Tom > GRS > > Hello Bobby, > > I was taught if there is a 5th floor it is not 13R. The whole building > has to be 13. > > Friday, April 18, 2008, 8:16:04 AM, you wrote: > > > A question has been asked in our office and I would appreciate the > opinions > > of the forum as to the intent of 13R. > > > There is a 5 story building, bottom floor is mercantile and the top 4 > > > floors are residential. "NFPA13R Standard for the Installation of > Sprinkler > > Systems in Residential Occupancies up to and Including Four Stories in > > > Height." The debate is; is the intent of the standard to be that > > anything over 4 stories cannot be classified as 13R or can the > > building in question be classified as 13R because there are 4 stories > > in height for residential occupancy? > > > > > > Thank you in advance. > > > > > > Bobby Gillett > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email > to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)