Not quite (at least in my opinion). 8.15.1.6 doesn't specify the hazard, so
it would apply for both LH and OH. But for some reason, the manufacturer
obtained listing for LH only. So whether you provide CC sprinklers in OH
occupancies or not,you lose. But I think the lesser evil is providing it.
I'm not on '07 yet, but ironing out issues for the future. If we talk about
this now, maybe, by the time '07 is implemented the CC will be listed for LH
and OH.

Tony  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: July 28, 2008 1:39 PM
To: [email protected]
Subject: RE: CC sprinklers

It's only in 2007. If the manufacture on list them as for use in light
hazard occupancy then by the wording of 8.15.1.6 doesn't apply because you
have an ordinary hazard situation. Don't you think?


Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Monday, July 28, 2008 2:53 PM
To: [email protected]
Subject: RE: CC sprinklers

This requirement is only for 2007, am I correct?

I've 2 other questions.

(1) Tyco cut sheets state this head is used for light hazard. If the area is
OH what happens? Sometimes a crawlspace is used as a mechanical room, with
tanks, pumps and other mechanical equipment.

(2) Sometimes a crawlspace is non-combustible with drywall attached to
bottom of wood joists or TJI's, but is required to be sprinklered due to
storage/mech. equipment etc. I would think 8.15.1.6 (07) should apply, but
is the wording clear? In this case, I think the 36" clearance is from floor
to ceiling (bottom of drywall) of the crawlspace. Right?

Tony 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt Willis
Sent: July 28, 2008 7:33 AM
To: [email protected]
Subject: FW: CC sprinklers

 

-----Original Message-----
From: Matt Willis
Sent: Monday, July 28, 2008 8:30 AM
To: '[email protected]'
Subject: RE: CC sprinklers

8.15.1.6 (07) 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Monday, July 28, 2008 8:14 AM
To: AFSA
Subject: CC sprinklers

Will someone please direct me to the section of NFPA13 2007 that covers the
circumstances requiring Tyco's CC sprinklers? I give up.

 

 

 

 

 

 

 

 

 

 

 

 

 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.138 / Virus Database: 270.5.6/1577 - Release Date: 7/28/2008
6:55 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to