Not quite (at least in my opinion). 8.15.1.6 doesn't specify the hazard, so it would apply for both LH and OH. But for some reason, the manufacturer obtained listing for LH only. So whether you provide CC sprinklers in OH occupancies or not,you lose. But I think the lesser evil is providing it. I'm not on '07 yet, but ironing out issues for the future. If we talk about this now, maybe, by the time '07 is implemented the CC will be listed for LH and OH.
Tony -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: July 28, 2008 1:39 PM To: [email protected] Subject: RE: CC sprinklers It's only in 2007. If the manufacture on list them as for use in light hazard occupancy then by the wording of 8.15.1.6 doesn't apply because you have an ordinary hazard situation. Don't you think? Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva Sent: Monday, July 28, 2008 2:53 PM To: [email protected] Subject: RE: CC sprinklers This requirement is only for 2007, am I correct? I've 2 other questions. (1) Tyco cut sheets state this head is used for light hazard. If the area is OH what happens? Sometimes a crawlspace is used as a mechanical room, with tanks, pumps and other mechanical equipment. (2) Sometimes a crawlspace is non-combustible with drywall attached to bottom of wood joists or TJI's, but is required to be sprinklered due to storage/mech. equipment etc. I would think 8.15.1.6 (07) should apply, but is the wording clear? In this case, I think the 36" clearance is from floor to ceiling (bottom of drywall) of the crawlspace. Right? Tony -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matt Willis Sent: July 28, 2008 7:33 AM To: [email protected] Subject: FW: CC sprinklers -----Original Message----- From: Matt Willis Sent: Monday, July 28, 2008 8:30 AM To: '[email protected]' Subject: RE: CC sprinklers 8.15.1.6 (07) -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Monday, July 28, 2008 8:14 AM To: AFSA Subject: CC sprinklers Will someone please direct me to the section of NFPA13 2007 that covers the circumstances requiring Tyco's CC sprinklers? I give up. Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - http://www.avg.com Version: 8.0.138 / Virus Database: 270.5.6/1577 - Release Date: 7/28/2008 6:55 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)