Joe, ask the AHJ for the section in 13 that says the flow test gpm must
equal or exceed the combined sprinkler/hose demand.  I may be wrong, but I
don't think it's there.

As a designer (yea, I know, I'm a REALLY a layout tech), I'd be nervous if
the sprinkler/hose demand was significantly greater than the test gpm, but
not 31 gpm.  If the potential error associated with a sprinkler/hose demand
that is equal to the test gpm would be deemed acceptable by the AHJ, the
additional potential error at 31 gpm beyond the test gpm just isn't
significant.

But maybe the simple mind of a layout tech can't comprehend such things.

Ed Kramer
Littleton, CO

 
> I have tried a new flow test with two 2-1/2" openings flowing and the
> pressure dropped off so that didn't work. I checked the coefficient and
> it
> is a .9. The hydrant does have a rounded inlet. I don't have play pipes
> and
> either does the city which is the only one that can do the test. I have
> tried different heads and pipes and nothing will drop my GPM to below
> the 31
> gpm we are short.
> 