John, what do you consider an appropriate place(s) to connect the sprinkler
piping to ensure a reliable connection to ground?  Just connecting it to the
nearest piece of metal might not suffice.
.
Ed Vining


On Wed, Jan 28, 2009 at 4:48 AM, John Drucker <[email protected]>wrote:

> Subject:   Grounding, Bonding and Sprinkler Piping
>
>
> >From an industry forum list (AFAA Firealarm). Apparently NFPA-25
> inspectors
> (contractors) are either removing the bonding connection and or noting it
> as
> a violation................................
>
> John
>
> --------------------------------------------------------------------------
>
> From: John Drucker <[email protected]>
> Subject: RE: [firealarm] Ground Rod Questions
>
> All interior water piping within a building, including metallic fire
> sprinkler piping is required to be bonded pursuant to 2008 NEC
> 250.104(A)(B)
> .
>
> Failure to bond a metallic piping system could result in the piping system
> becoming energized with the potential of shock or electrocution. Bonding
> merely places all metallic components within a building at
> equipotential.These components, water piping, gas piping, building steel,
> etc are bonded (electrically connected together) to the electrical system.
> A
> properly bonded system assures a low impedance electrical path exists
> should
> a fault occur producing the needed fault current in order to operate a
> circuits overcurrent device thus clearing the fault by deenergizing the
> circuit.
>
> Grounding on the other hand is the connection of the buildings electrical
> system to earth in order to dissipate lighting, transients and stabilize
> system voltage. Grounding is not Bonding. The sprinkler piping prohibition
> applies to the use of fire sprinkler piping as a Grounding electrode. Its
> important that we not remove bonding jumpers from aboveground fire
> sprinkler
> piping. If you're not sure consult with your electrical inspector. In the
> end it might just save someone's life !
>
> Sincerely,
>
> John Drucker
>