I agree, but to what should the ground/bonding wire from the riser be
connected?

On Wed, Jan 28, 2009 at 8:48 AM, John Drucker <[email protected]>wrote:

> Ed,
>
> In my professional opinion I would say the riser after any backflow
> devices, fire pumps, alarm and check valves, i.e. items that are
> expected to be removed for repair or replacement, however the code does
> not stipulate this.  In all cases the electrical engineer and local
> inspector are to be consulted.
>
> Hope that helps.
>
> John Drucker
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ed Vining
> Sent: Wednesday, January 28, 2009 11:13 AM
> To: [email protected]
> Subject: Re: FW: Grounding, Bonding and Sprinkler Piping
>
> John, what do you consider an appropriate place(s) to connect the
> sprinkler piping to ensure a reliable connection to ground?  Just
> connecting it to the nearest piece of metal might not suffice.
> .
> Ed Vining
>
>
> On Wed, Jan 28, 2009 at 4:48 AM, John Drucker
> <[email protected]>wrote:
>
> > Subject:   Grounding, Bonding and Sprinkler Piping
> >
> >
> > >From an industry forum list (AFAA Firealarm). Apparently NFPA-25
> > inspectors
> > (contractors) are either removing the bonding connection and or noting
>
> > it as a violation................................
> >
> > John
> >
> > ----------------------------------------------------------------------
> > ----
> >
> > From: John Drucker <[email protected]>
> > Subject: RE: [firealarm] Ground Rod Questions
> >
> > All interior water piping within a building, including metallic fire
> > sprinkler piping is required to be bonded pursuant to 2008 NEC
> > 250.104(A)(B)
> > .
> >
> > Failure to bond a metallic piping system could result in the piping
> > system becoming energized with the potential of shock or
> > electrocution. Bonding merely places all metallic components within a
> > building at equipotential.These components, water piping, gas piping,
> > building steel, etc are bonded (electrically connected together) to
> the electrical system.
> > A
> > properly bonded system assures a low impedance electrical path exists
> > should a fault occur producing the needed fault current in order to
> > operate a circuits overcurrent device thus clearing the fault by
> > deenergizing the circuit.
> >
> > Grounding on the other hand is the connection of the buildings
> > electrical system to earth in order to dissipate lighting, transients
> > and stabilize system voltage. Grounding is not Bonding. The sprinkler
> > piping prohibition applies to the use of fire sprinkler piping as a
> > Grounding electrode. Its important that we not remove bonding jumpers
> > from aboveground fire sprinkler piping. If you're not sure consult
> > with your electrical inspector. In the end it might just save
> > someone's life !
> >
> > Sincerely,
> >
> > John Drucker
> >
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
> CONFIDENTIAL AND PROPRIETARY:
> This email message is intended only for the use of the individual or entity
> to which it is addressed and may contain information that is privileged and
> confidential, nor is it, unless specifically stated, intended to be relied
> upon by any person or persons other than the individual or entity named
> above and no warranties or representations are made or intended to persons
> or entities not named above.  If the reader is not the intended recipient,
> you are hereby notified that any dissemination, distribution or copying of
> this communication is strictly prohibited.  If you have received this
> communication in error, please notify us immediately by telephone, return
> this message to the address above and delete all copies.  Thank you.
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to