I note it because it is a foreign item attached to my sprinkler which is
prohibited. Not unlike a coat hanger on a head or a sign hanging from a BL.
Now perhaps in theory world the owner has a letter from a PE and approval
from an AHJ to hang such a banner but you still note it.  

13 - 25 says grounding prohibited but doesn't say bonding is
allowed/required right?  It's the owner's problem to figure out if
allowed/required by other code requirements.  

Here's the down side of not noting it.  Let's say it is grounding and
something goes wrong and there is an electrical caused problem that results
in injury or property damage. Are you also brought in to the claim because
you didn't note it in clear violation of the standard and had you noted it
(and it was corrected) the incident wouldn't have occurred?  True the guy
who connected was wrong in the first place but you were also wrong in not
bringing it up.  With one note on an inspection you are out of the claim
quickly without costs of defense and a chance the jury or settlement
conference lays it off on you because the electrician is long gone.  I don't
know but I think you are ALWAYS safer for bringing things up and documenting
them than not.          

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, January 28, 2009 1:20 PM
To: [email protected]
Subject: Re: FW: Grounding, Bonding and Sprinkler Piping

No you should not note it. That is outside the scope of an NFPA 25
insoection. 
>From my understanding, you would have more exposure to liability by noting
it than not noting it. 
Forest Wilson
Cherokee Fire
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Chris Cahill" <[email protected]>

Date: Wed, 28 Jan 2009 12:30:25 
To: <[email protected]>
Subject: RE: FW: Grounding, Bonding and Sprinkler Piping


I'll show some ignorance because I have never seen a wire attached to a
sprinkler system.  How would I tell the difference between a ground
connection and a bond connection?  Wouldn't they both be a clamp and wire
running off to who knows where?  Isn't it the where that make the difference
between the two not the clamp?

So if they appear the same to the sprinkler contractor they indeed then
should all be noted on all inspections.  The owner then in theory confirms
ground or bond.  I note it again every year for CYA?

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, January 28, 2009 11:54 AM
To: [email protected]
Subject: RE: FW: Grounding, Bonding and Sprinkler Piping

Thom,

Even in the electrical industry there is much confusion over bonding and
grounding. Suffice to say that outside the electrical industry it would be
expected to be more so. As with all other matters if ones not sure, ask
questions of someone qualified to make the determination.

I have experienced first hand sprinkler mechanics and inspectors removing
bonding and grounding connections from sprinkler systems. First and foremost
consider the ramifications. 

If it's a ground connection where the piping is being used as a grounding
electrode, a violation of NFPA-13, removal of the grounding electrode
conductor worsens the situation since a grounding point, albeit in
violation, is nonetheless lost exposing the buildings electrical system. The
correct and safe process would be to report the possible violation so that a
proper grounding electrode could be provided and connected before removing
the improper one.

If it's a bonding connection removal the potential exists for the piping to
become energized without the ability to clear a fault, exposing anyone
including sprinkler and fire department personnel to the risk of death or
injury. Again the correct and safe process would be to report the possible
violation so that an electrical contractor or inspector can make an educated
determination.

Interesting how this originated on the fire alarm list, but not to worry
we're in this together !   Now back to 2009 IRC already in progress. 

Sincerely,

John Drucker
Fire Protection Subcode Official
Electrical Inspector
Licensed Electrical Contractor

Safe Buildings Save Lives !



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Wednesday, January 28, 2009 12:29 PM
To: [email protected]
Subject: RE: FW: Grounding, Bonding and Sprinkler Piping

Grounding of the sprinkler riser is prohibited. 10.6.8* In no case shall the
underground piping be used as a
grounding electrode for electrical systems. This does not preclude
the bonding of the underground piping to the lightning
protection grounding system as required by NFPA780 in those
cases where lightning protection is provided for the structure.
 We're talking "Bonding" for Ground fault and Arc fault operation inside of
the structure or building. Since this falls under the NEC the electrical
engineer and electrical contractor are responsible for the installation of
all "Bonds" to all metallic building systems. I believe the purpose of this
entire post has been to make everyone, AHJ, Contractor or inspectors, aware
that a bond is required at some location. That a bond is not a ground. And
that this will not fall under the "Hang or support nothing from the
sprinkler piping or hangers" Additionally in seismic areas this "Bond" must
be of sufficient length and flexibility to allow for differential movement,
depending upon its location.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Wednesday, January 28, 2009 9:59 AM
To: [email protected]
Subject: RE: FW: Grounding, Bonding and Sprinkler Piping

Remember, that for it to be considered a ground, NFPA #70 requires 10' of
continuous cover on the pipe. If it is plastic, such as the run up to the
stub on most sprinkler systems, then this will not meet the definition.

R/

Matt

Matthew J. Willis
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, January 28, 2009 10:49 AM
To: [email protected]
Subject: RE: FW: Grounding, Bonding and Sprinkler Piping

Ed,

In my professional opinion I would say the riser after any backflow devices,
fire pumps, alarm and check valves, i.e. items that are expected to be
removed for repair or replacement, however the code does not stipulate this.
In all cases the electrical engineer and local inspector are to be
consulted.

Hope that helps.

John Drucker

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Vining
Sent: Wednesday, January 28, 2009 11:13 AM
To: [email protected]
Subject: Re: FW: Grounding, Bonding and Sprinkler Piping

John, what do you consider an appropriate place(s) to connect the sprinkler
piping to ensure a reliable connection to ground?  Just connecting it to the
nearest piece of metal might not suffice.
.
Ed Vining


On Wed, Jan 28, 2009 at 4:48 AM, John Drucker
<[email protected]>wrote:

> Subject:   Grounding, Bonding and Sprinkler Piping
>
>
> >From an industry forum list (AFAA Firealarm). Apparently NFPA-25
> inspectors
> (contractors) are either removing the bonding connection and or noting

> it as a violation................................
>
> John
>
> ----------------------------------------------------------------------
> ----
>
> From: John Drucker <[email protected]>
> Subject: RE: [firealarm] Ground Rod Questions
>
> All interior water piping within a building, including metallic fire 
> sprinkler piping is required to be bonded pursuant to 2008 NEC
> 250.104(A)(B)
> .
>
> Failure to bond a metallic piping system could result in the piping 
> system becoming energized with the potential of shock or 
> electrocution. Bonding merely places all metallic components within a 
> building at equipotential.These components, water piping, gas piping, 
> building steel, etc are bonded (electrically connected together) to
the electrical system.
> A
> properly bonded system assures a low impedance electrical path exists 
> should a fault occur producing the needed fault current in order to 
> operate a circuits overcurrent device thus clearing the fault by 
> deenergizing the circuit.
>
> Grounding on the other hand is the connection of the buildings 
> electrical system to earth in order to dissipate lighting, transients 
> and stabilize system voltage. Grounding is not Bonding. The sprinkler 
> piping prohibition applies to the use of fire sprinkler piping as a 
> Grounding electrode. Its important that we not remove bonding jumpers 
> from aboveground fire sprinkler piping. If you're not sure consult 
> with your electrical inspector. In the end it might just save 
> someone's life !
>
> Sincerely,
>
> John Drucker
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity
to which it is addressed and may contain information that is privileged and
confidential, nor is it, unless specifically stated, intended to be relied
upon by any person or persons other than the individual or entity named
above and no warranties or representations are made or intended to persons
or entities not named above.  If the reader is not the intended recipient,
you are hereby notified that any dissemination, distribution or copying of
this communication is strictly prohibited.  If you have received this
communication in error, please notify us immediately by telephone, return
this message to the address above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]