45 ft. is the limit for ESFR. If the building isn't storage why use a
storage sprinkler instead of area density?

Tyco is suppose to be coming out with Kbig ESFR for buildings above 45
ft but I don't know if it will go to 55 ft. It may stop at 50 if it
comes out all.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dennis
Browning
Sent: Thursday, February 12, 2009 12:40 PM
To: [email protected]
Subject: ESFR Systems

I have a 54' tall building that the owner is suggesting ESFR system
design. Is there a limit on building height for that type system. This
building will NOT have rack or high piled storage.

Dennis Browning
Browning Fire
Medford, Oregon