There have been some heated debates on this issue.  I have a White Paper which 
outlined numerous testing scenarios with vents, curtains and sprinklers.  


Here is the Conclusion of the research.


INTERACTION OF SPRINKLERS WITH SMOKE AND HEAT VENTS
Craig L. Beyler and Leonard Y. Cooper
Hughes Associates, Inc. - Fire Science and Engineering
Baltimore, Maryland  1999

"CONCLUSIONS
The studies of smoke and heat venting used in conjunction with sprinklers show 
clearly that
venting does not have a negative effect on sprinkler performance. Successful 
performance of
sprinklers does not rely upon reduced oxygen concentrations. Venting has been 
shown to have
no effect on the activation times of early sprinklers and does not affect the 
total number of
sprinklers activated. If the fire is directly beneath a vent, activations of 
the first sprinklers may
be delayed slightly, but there is no evidence that this will have a significant 
impact on sprinkler
performance.
Experimental studies have shown that venting does limit the spread of products 
of combustion by
releasing them from the building within the curtained compartment of fire 
origin. This improves
visibility for building occupants and firefighters who need to find the seat of 
the fire to complete
fire extinguishment. Limiting the spread of smoke and heat also reduces smoke 
and heat damage 
to the building. In the event that sprinklers do not operate, venting remains a 
valuable aid to
manual control of the fire.
The experimental studies have shown that early vent activation has no 
detrimental effects on
sprinkler performance and have also shown that current design practices are 
likely to limit the
number of vents operated to one and vents may in fact not operate at all in 
very successful
sprinkler operations. Design practices should move to methods which assure 
early operation of
vents, and vent operation should be ganged so that the benefit of roof vents is 
fully realized.
Sprinkler design with vents and draft curtains needs to take full account of 
draft curtains as
obstructions. Curtains should be placed in aisles rather than over storage."



If anyone would like the full text which includes the various testing 
scenarios, e-mail me and I'll send you a copy.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to